3/14/2023 2:25 PM | |
Joined: 3/14/2023 Last visit: 3/14/2023 Posts: 1 Rating: (0) |
I have F011 couple times a day usually when motor have more load. r785 recorded -7.5, -11, -25, +6.5, +11, +7.5A during the fault and motor is rated 14A and has been running OK for last 15years till now. No mechanical issues found, motor running balanced 6-11A depends on load, no noises, no binding, motor meg OK, encoder appear to be working, breaking resistor measured OK, breaking unit was replaced. Repetition of the faults seem to be decreased but still faulting F011. What else can i check? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/15/2023 08:12:38New subject after splitting |
|
3/17/2023 5:01 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (873)
|
Hello, You can use trace recording function for further trouble shooting by selecting appropriate parameters & trigger levels. Please refer manuals under this link. |