10/20/2020 5:31 PM | |
Joined: 9/27/2006 Last visit: 5/22/2024 Posts: 12257 Rating: (2668) |
Hello Voltron; In the case of redundant CPUs, the following document does state that you need to establish double-sided redundancy connections, which would require using MB_RED_Server and MB_RED_Client, as I understand it. https://support.industry.siemens.com/cs/lu/en/view/109755202/112744387339 However, I agree that your case might be different, and that you might be able to use single-sided redundancy, as you determined. But I cannot at this point push for one solution over another. I would suggest you ask Siemens techs for a decision, using a Support Request (link at the top of this page). And I, for one, would be most interested in their reply and suggestions. Hope thios helps, |
Last edited by: dchartier at: 10/20/2020 17:35:24 |
|
8/21/2023 8:24 AM | |
Joined: 5/23/2023 Last visit: 4/19/2024 Posts: 3 Rating: (0) |
Hello, Did you find the solution? Which HW ID is neccesary to add? Regards, AR |