12/22/2022 12:54 PM | |
Joined: 3/11/2019 Last visit: 6/4/2024 Posts: 1453 Rating: (263) |
Hi, as already mentoined the Interference voltage suppression for interference frequency should be set to the power supply freqency, in this case 50Hz. But no, the configured interference frequency directly effects the integration/basic conversion time of the channel. So if you set 400Hz, this will result in a faster integration/conversion time. But you may run into troubles with the quality of the signal as the frequency differs from the power supply. Maybe the following FAQ can help. The FAQ is written for another module, so the values will not match your module. But the principle is the same. How do you calculate the cycle time of the analog input module AI 2xU/I 2-/4-wire HF of the ET 200SP depending on the parameterized interference frequency suppression and what influence does this have on a digital filtering via a smoothing factor?regars sancruz |
Feedback appreciated, please rate |
|
Follow us on