5/3/2024 4:12 PM | |
Joined: 2/1/2010 Last visit: 5/20/2024 Posts: 139 Rating: (68) |
Moltoff's recommendation might be a valid way to do it, but I would suggest against it since then you can't use feature bits 2 or 23. Also I'm pretty sure, that changing the status byte to FF externally it also makes the interlock voting work in unexpected ways (ie makes the input not vote). So you would basically need to have two copies of the interlocks, one for display, and one for actual tripping. It sounds like you want to make a custom solution and not the default behavior, perhaps as a custom faceplate or popup graphic to display all the interlocks at once and not just by opening each interlock faceplate linked. In this case you can make use of the Status1 - Status8 outputs from the Interlock blocks and do custom animations. (check the help file to understand each function) If you want the list to shrink in size to not have big gaps between the active ones, you are going to need to be comfortable with scripting in WinCC. I can't offer you examples here at this time as this is a pretty big effort to undertake. |
Last edited by: RVS.wick at: 05/03/2024 16:29:27If my post helped you, please rate. Thanks. |
|
This contribution was helpful to1 thankful Users |
Follow us on