in TIA Selection Tool, make sure you have the newest version if using desktop version. Set the properties for the whole Rack from the main page and select without power bus. (working in desktop version) I didn't try online version with this feature. As for usage questions: 1. Nothing is required in HW config. 2.For using D-Sub, each module is automatically its own power bus, there is no option to use previous. Also if you are using the Siemens D-Sub base (e.g. H0) you have to supply power to the auxiliary terminals on the base. If you use the Phoenix D-Sub adapter that plugs into standard base (e.g. H1), you can use the auxiliary terminals or the power terminals at the Phoenix VIP terminal. The Siemens D-Sub does not connect the 24V through the D-Sub header, which is annoying. |