5/16/2022 8:44 AM | |
Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (296) |
Hello, first of all: I have never done that and also not tested it with a G120 drive. But you can do such configurations in general with the so called Data Sets and switchover between them. I hope you just have one motor at the same time connected to the drive and not two different ones at the same time in parallel, do you? Here is how you can configure it in Startdrive: 1. Create a second Drive Data Set (see my screenshot 00) 2. Select Data Set 0 in the top and go through the commissioning wizard to enter your motor data of the first motor 3. Select Data Set 1 in the top and again go through the commissioning wizard to enter your motor data of the second motor In p820 you can select a signal source to switch over between the 2 data sets - you could either use a Digital input or you select a free control bit from the control word of the PZD so you can change it from the PLC side. Attachmenttwo_motors_at_g120.zip (614 Downloads) |
Best regards, |
|
This contribution was helpful to3 thankful Users |
9/10/2022 12:34 PM | |
Joined: 6/24/2022 Last visit: 7/16/2023 Posts: 3 Rating: (0) |
Hello How could you make the plc choose the right dds ? |