4/24/2024 12:24 PM | |
Joined: 4/14/2018 Last visit: 5/20/2024 Posts: 42 Rating: (1) |
Hello, Try ✅TIA V17 or higher for firmware 2.9, I am attaching the data sheet, the same is mentioned there. Attachment6ES75163AN010AB0_datasheet_en.pdf (4 Downloads) |
|
|
4/24/2024 1:17 PM | |
Joined: 1/21/2013 Last visit: 5/20/2024 Posts: 2798 Rating: (452)
|
Hi maint42, STEP 7 V14 SP1 supports S7-1500 PLCs up to V2.1, the successor firmware version V2.5 requires at least STEP 7 V15. Since you wrote that you can only select V2.0, I assume that this is because you want to change the device. And a V2.1 device - without changing the type - can only be upgraded to a previous firmware version, because there is no newer one available. However, a PLC with a newer firmware version installed than the one configured can still be used. However, your problems may be due to instruction versions that can also be changed for your PLC code. You may want to check this. If this does not help, providing a screenshot may help the community to understand your problem. Kind regards |