8/17/2016 2:43 PM | |
Posts: 7 Rating: (0) |
Dear sir CPU 317 - 2DP (6ES7 317-2AJ10-0AB0) was phase out. So i changed to CPU 317 -2DP (6ES7 317-AK14-0AB0) but it shows SF & BF Please help me to solve the issue Regards PLC Engr Diagnostic buffer of module CPU 317-2 DP Order No./ Description Component Version 6ES7 317-2AK14-0AB0 Hardware 1 - - - Firmware V 3.3.7 Boot Loader Firmware expansion A 33.9.9 Rack: 0 Slot: 2 Serial number: S C-C8VP24512012 Event 1 of 10: Event ID 16# 2943 I/O access error, writing P area, byte access, Access address: 625 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0010 0271 0000 0000) Event 2 of 10: Event ID 16# 2943 I/O access error, writing P area, byte access, Access address: 624 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0010 0270 0000 0000) Event 3 of 10: Event ID 16# 2943 I/O access error, writing P area, byte access, Access address: 623 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0010 026F 0000 0000) Event 4 of 10: Event ID 16# 2943 I/O access error, writing P area, byte access, Access address: 622 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0010 026E 0000 0000) Event 5 of 10: Event ID 16# 2943 I/O access error, writing P area, byte access, Access address: 621 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0010 026D 0000 0000) Event 6 of 10: Event ID 16# 2943 I/O access error, writing P area, word access, Access address: 618 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0020 026A 0000 0000) Event 7 of 10: Event ID 16# 2943 I/O access error, writing P area, word access, Access address: 616 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.687 AM 12/23/1994 (Coding: 16# 2943 017A 0020 0268 0000 0000) Event 8 of 10: Event ID 16# 2943 I/O access error, writing P area, word access, Access address: 614 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.686 AM 12/23/1994 (Coding: 16# 2943 017A 0020 0266 0000 0000) Event 9 of 10: Event ID 16# 2943 I/O access error, writing P area, word access, Access address: 612 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.686 AM 12/23/1994 (Coding: 16# 2943 017A 0020 0264 0000 0000) Event 10 of 10: Event ID 16# 2943 I/O access error, writing P area, word access, Access address: 610 Requested OB: I/O access error OB (OB122) Priority class: 1 External error, Incoming event 09:21:57.686 AM 12/23/1994 (Coding: 16# 2943 017A 0020 0262 0000 0000) ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 8/18/2016 1:03:10 PMNew subject after splitting |
|
8/19/2016 8:01 AM | |
Posts: 7 Rating: (0) |
Hello sir Thanks for your reply.. i just go to HW configuration and click the replace option & Replace the CPU from 6ES7-317-2AJ10-0AB0-to 6ES7-317-AK14-0AB0 I won't change the IO readdress.. I am very new person for siemens plc So please give advise to solve the issue... Before and after configuration screen shot attached.. Thanks & Regards HSMIPLC AttachmentCPU CHANGE.xlsx (308 Downloads) |
8/19/2016 12:54 PM | |
Joined: 11/29/2011 Last visit: 5/20/2024 Posts: 1358 Rating: (231) |
Hi, The way I look at it, the address entered into your Diag buffer not present on the screen you attached. So the above comment probably a good lead. The CPU may be an I-Device, and the IO addresses not accessable. You need to make sure that the "DP Master System" get the updated with the "new slave". See theHow do you add a CPU as DP slave to the DP master system of a different CPU whereby the CPUs are configured in different STEP 7 projects? for guidance. Let us known how you getting on! |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to1 thankful Users |
8/20/2016 10:07 AM | |
Posts: 7 Rating: (0) |
Hi... In DP master system CP -342-5 only assigned. How can i update the DP slave CPU type??? Thanks & Regards HSMIPLC Attachmentcp module.xlsx (205 Downloads) |
1/6/2024 7:02 AM | |
Joined: 3/15/2017 Last visit: 1/6/2024 Posts: 4 Rating: (0) |
Having the same problem after replacing cpu can anyone help please. Attaching some photos |