1/13/2021 10:55 AM | |
Joined: 8/8/2019 Last visit: 3/10/2023 Posts: 5 Rating: (0) |
Some additional information about the settings and diagnostics buffer |
1/13/2021 10:55 AM | |
Joined: 8/8/2019 Last visit: 3/10/2023 Posts: 5 Rating: (0) |
Some additional information about the settings and diagnostics buffer |
12/16/2021 9:04 AM | |
Joined: 9/3/2008 Last visit: 5/8/2024 Posts: 921 Rating: (158) |
Hi, I had the same experience with cpus in fw 2.8 and panels before image v17. I found that the way they poll the ntp server is send a request for time, four times in a row. Some ntp servers are set up to not allow this. It is a setting to avoid overload. If you can configure the ntp server, it is possible to set it to allow this. This should be fixed with cpu fw. 2.9 and panels image 17. I have tested cpu fw 2.9 and it works, but I have not tested panel image v17 yet. This may be the issue you have. You can probably only check this with a Wireshark trace. See How do you configure the "Port Mirroring" to monitor network traffic. |
Last edited by: Michael K at: 12/16/2021 09:05:52Michael |
|
3/27/2024 4:38 PM | |
Joined: 1/23/2024 Last visit: 4/19/2024 Posts: 2 Rating: (0) |
I have the same problem and have not found any solution. |