Thread Starter: shivsharma   Started: 6/22/2012 7:36 AM   Replies: 6

« Previous thread Next thread »
Page 1 of 1 (7 items)
  6/22/2012, 7:36 AM
Joined 3/30/2012
Last visit: 3/30/2013
Posts: 38
Rating:
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi
I have a transformer of 600V AC Ouput. Can I Use Drive Whose Input Voltage Rating 3phase 690V AC on the Above mentioned Transformer without any harm or i shall use a transforer whose output shall be 690V AC.?



=== Edited by shivsharma @ 6/22/2012 9:05 AM [GMT ] ===


Top
  6/22/2012, 4:07 PM
Joined 8/8/2011
Last visit: 4/22/2014
Posts: 179
Rating:
Rated: Excellent [4.06 out of 5 / rated 33 time(s)]. (33) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello shivsharma,

The answer to your question depends upon the specific input voltage operating range for the drive. 

Drives are normally rated to operate within a specific voltage range.

If drive is rated to operate with input voltage in range of 600 VAC to 690 VAC then the 600 VAC transformer output voltage would be acceptable for drive itself. 

However, due to the 600 VAC input you may not be able to achieve the maximum amount of power out of drive to motor to perform application (i.e. due to the lower input voltage the output voltage to motor will be lower and more current will be needed through motor to perform application).

Deputy
Top
  6/23/2012, 6:06 AM
Joined 3/30/2012
Last visit: 3/30/2013
Posts: 38
Rating:
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Sir
Our Motor Max. Armature Voltage is 600V DC.I want to know That If i Use 690V Input Supply drive on 600V AC Supply,What will be The Effect. And Our Source Capacity(Transformer) is Sufficient To deliver required Amount of Power To drive.
Top
  6/29/2012, 12:20 PM
Joined 4/23/2010
Last visit: 4/22/2014
Posts: 1540
Rating:
Rated: Outstanding [3.58 out of 5 / rated 72 time(s)]. (72) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Can you provide complete motor nameplate & drive MLFB details?

Tell me and I will forget. Show me and I will remember. Involve me and I will understand. -Confucius
Top
  6/30/2012, 1:19 PM
Joined 3/30/2012
Last visit: 3/30/2013
Posts: 38
Rating:
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Sir

DC Motor Details As:
Type: NP400KXSPVA/83    Duty-S1  IP-23
KW            870       
Va              600V DC
Ia                    1549/1720
Vf                   330
If                13/5.6         
RPM           930/1800


Now We Want to Select The Converter for This Motor . We have Source of Supply Voltage  600V AC. So What Shall be the Converter Specification For Trouble free Operation?
Top
  7/1/2012, 9:23 AM
Joined 4/23/2010
Last visit: 4/22/2014
Posts: 1540
Rating:
Rated: Outstanding [3.58 out of 5 / rated 72 time(s)]. (72) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,
I would like to suggest you to check 6RA7095-6 or 4 KV62. Please see the attached sheet. Please note the drive selection also depends options to be selected depending upon number of digital I/Os, any other specific logic if needed, technology etc. I would recomend you to contact your near Siemens RSC for more information. Please check the manual of 6RA70 here for more information. Also please check the transformer configuration & drive AC power requirement, power losses & actual application load power demand requirements.

Attachment: 6RA70 order data sheet.pdf  (11 Downloads)

Tell me and I will forget. Show me and I will remember. Involve me and I will understand. -Confucius

Top
  7/2/2012, 7:37 AM
Joined 3/30/2012
Last visit: 3/30/2013
Posts: 38
Rating:
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks
Top