Dear PISCEAN
Do you know the fault level at Transformer end
For example, if you are having a fault level of 50 kA means,
try to select the ABB (just in output side of transformer) also 50 kA
try to select the ABB (800 A at OLD shop) also 50 kA
try to select the ABB (800 A at OLD shop @ Power House) as 35 kA
try to select the 630A MCCB as 35 kA
Further downstreams are 20 kA, 10 kA and 6 kA so on.
it is clarified your doubt or kindly revert me.