Hello ssmanku1699 you have a few options to achive your goal: 1.) Assuming your 313C'sDP port is NOTneeded as a DP Master, you configure it forDP Slave mode and add an IE/PB Link to it as the Gateway to the Profinet I/O Controller. 2.) Add a CP343-1 to the 313C system and configure it asa Profinet I/O device. 3.)If your 313C'sDP port is used as aDP Masterport, you could stillgo with option 1 but will need to add a DP/DP coupler additionally (least favourite option to be honest, purely mentioned for completeness). And here are a few selected example links with more on the above: Where do you find sample programs and documentation on communication between S7-400 (PROFINET IO controller) and S7-300 (I slave) incorporating an IE-to-PB link gateway? Where can you find information on the topic of PROFINET? How do you program communication blocks FC11 and FC12 for the PROFINET IO device? I hope this helps |