Hello,

Is it possible to make hot swap of modules in any S7 system? I always turn off 300 modules before setting any new one and then while insertin HW config it goes stp again. If I am right that is the same procedure with s7-400. Dont you think it sholud be possible to make it all on-line? Is it going to be possible to make so with s7-1200?

best regards



=== Edited by O_Moderator @ 6/3/2011 9:34 AM [GMT ] ===
question corrected

Top
  6/1/2011, 4:39 PM
Joined 7/2/2008
Last visit: 10/19/2014
Posts: 796
Rating:
Rated: Excellent [4.25 out of 5 / rated 228 time(s)]. (228) 
Users with special expertise supervising conferences
Rated: Excellent [4.5 out of 5 / rated 2 time(s)]. (2) 
Hello Oscar_83PL,

Oscar_83PL wrote:
Is it possible to make hot swap of modules in any S7 system?
Yes it is.
Hot swapping (replacing module online) is available in S7-400 CPU whether you work with central modules (S7-400) or S7-300 modules (Profibus & Profinet).

With S7-300 CPU, it's available but just with Profinet.
Or maybe you can use the trick mentioned here
wrote:
If I/O modules (in the ET200M) are inserted or removed during operation, then OB83 is called. But this OB is not supported by the CPUs of the S7-300 series, because it is not available in the CPU operating system. If the ET200M is configured as standard slave in STEP7 (via the GSD file), then Insert/Remove is possible, because in this case it is not OB83 but OB82 that is called. This OB is supported by all S7-300/400 CPUs


Best regards.

H-H



=== Edited by H-H @ 6/1/2011 4:41 PM [GMT ] ===


Top
Thank you for this post from:
  6/1/2011, 7:03 PM
Joined 8/5/2009
Last visit: 7/29/2014
Posts: 124
Rating:
Rated: Outstanding [4 out of 5 / rated 2 time(s)]. (2) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I don't know much about hotswap possibillities

But I just worked with a new type S7 CPU

6ES7 315-2EH14 V3.2.3


This CPU has Profinet IO

If you look at the online Technical data it is possible to use OB83 (only for Profinet IO )

Technical data new 315 PN DP
Top
  6/1/2011, 7:43 PM
Joined 9/27/2005
Last visit: 7/5/2013
Posts: 948
Rating:
Rated: Above avarage [2.68 out of 5 / rated 37 time(s)]. (37) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi!

Hotswap theoretical possible - if CPU has OB83. Then should see details.
 
As sample for  CPU I 6ES7 315-2EH14 V3.2.3 see in technical data
possible to use OB83 only for Profinet IO . This is due to the fact that when inserting / removing a module called OB83, and your the program can correctly handle of the change configuration
Top
  6/2/2011, 8:42 AM
Joined 10/22/2008
Last visit: 10/21/2014
Posts: 316
Rating:
Rated: Excellent [4.25 out of 5 / rated 4 time(s)]. (4) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
If I understand Your posts I see it is not possible to make simple module swap. There is another problem if you want to change module with different order number. Ex. DI16 change to DI32. You still have to update firmaware and this operation is not allowed in RUN state.
Top
  6/2/2011, 9:08 AM
Joined 10/7/2005
Last visit: 10/24/2014
Posts: 2574
Rating:
Rated: Excellent [4.29 out of 5 / rated 716 time(s)]. (716) 
Users with special expertise supervising conferences
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Oscar_83PL wrote:
... I see it is not possible to make simple module swap. There is another problem if you want to change module with different order number.

you can swap, add and/or reconfigure in RUN with CIR (Configuration in Run) dear Oscar_83PL and you'll find all the relevant info (what hardware is supported/needed, what is possible and what isn't) in the manuals and links below:
SIMATIC STEP7 V5.5 Modifying the System during Operation via CiR manual
Which DP slaves can be added to and removed from a PROFIBUS DP master system using the CiR function (Configuration in RUN) and which configuration changes are permissible?
What should you watch out for when adding components or changing their parameters using CiR (Configuration in Run)?
What should you watch out for when using the "Configuration in Run" (CiR) function on the PROFINET IO system?

Cheers

fritz

The advice and opinion given in this thread is that of the author and does not necessarily reflect the views of I S Systems Pty Limited.
To find out how I S Systems can help you with your automation needs please visit www.issystems.com.au.
Top
Thank you for this post from:
H-H
  6/3/2011, 8:15 PM
Joined 9/27/2005
Last visit: 7/5/2013
Posts: 948
Rating:
Rated: Above avarage [2.68 out of 5 / rated 37 time(s)]. (37) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello!

I believe that CiR  is only available for CPU4xx or am I wrong?
Top
  6/4/2011, 2:26 AM
Joined 7/2/2008
Last visit: 10/19/2014
Posts: 796
Rating:
Rated: Excellent [4.25 out of 5 / rated 228 time(s)]. (228) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello gre_m,

No, you are not.
The CIR is only available with S7-400 CPUs.

Best regards.

H-H
Top
  6/4/2011, 6:20 PM
Joined 9/27/2005
Last visit: 7/5/2013
Posts: 948
Rating:
Rated: Above avarage [2.68 out of 5 / rated 37 time(s)]. (37) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello
I understand your reply.  I wanted to say "The CIR is only available with S7-400 CPUs". May be defect translate.



=== Edited by gre_m @ 6/4/2011 6:22 PM [GMT ] ===


Top
  6/5/2011, 12:36 PM
Joined 1/7/2006
Last visit: 10/22/2014
Posts: 2674
Rating:
Rated: Excellent [4.07 out of 5 / rated 258 time(s)]. (258) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

Maybe don't use the questiomark at the end grin

I hope that the answer will help, if you have still questions, don't hesitate to ask me.

All the best, Late
Never say never, think in solutions, not in trouble......