Technical Forum

Low-Voltage Power Distribution and Installation Technology

Distinction between mpcb, mccb, mcb

Thread Starter: maulik   Started: 1/6/2008 11:55 AM   Replies: 20

« Previous thread Next thread »
Page 1 of 1 (21 items)
  1/6/2008, 11:55 AM
Joined 1/6/2008
Last visit: 1/19/2008
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear ALL,

 I am new to this field and am not quite clear about the exact functional difference between a mcb, mccb, mpcb.

All are for protection and if some document is available that explains the same ???

I have basic idea about each but dont undestand the distinctions.

Thanking you in anticipation.

Maulik
Top
  1/16/2008, 9:45 AM
Joined 8/21/2007
Last visit: 5/15/2013
Posts: 352
Rating:
Rated: Excellent [4.61 out of 5 / rated 23 time(s)]. (23) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
hello maulik,
I want to send you a broshure with all informations you need.
But it´s to big to attach it in this reply.
Please give me an e-mail adress where I can can send it to, or contact
technical-assistance@siemens.com
regards
LesPaul
Top
  1/19/2008, 11:27 AM
Joined 1/6/2008
Last visit: 1/19/2008
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hey, Thank you very much for your concern and prompt reply.

Thanking you in anticipation



=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted

Top
  4/15/2008, 1:02 PM
Joined 2/27/2008
Last visit: 12/21/2010
Posts: 148
Rating:
Rated: Outstanding [3.63 out of 5 / rated 8 time(s)]. (8) 
Rated: Excellent [4.5 out of 5 / rated 2 time(s)]. (2) 

Have this short info.
In the world of Circuit Protection Devices, people tend to use a lot of abbreviations and acronyms that sometimes leave readers with confusion because they may be different from what they have been taught or picked up along the way. Thist hread will list the common terms ands provide brief descriptions to help untangle some of the confusion. This is intended to be a work in progress, please feel free to make suggestions for additions or deletions. I am using two terms that need a little definition: "NEMA world" refers to North America, i.e. USA and Canada (and to a lesser extent, Mexico) where standards are developed by NEMA (National Electrical Manufacturers Association) and acceptance testing is done by UL. "IEC world" basically refers to most of the rest of the world that adheres to the standards put forth by the International Electotechnical Commission, who's manufacturers generally self-regulate and test. I will start off randomly and eventually reorganize it in alphabetic order.

MCB In NEMA world, this used to exclusively mean "Main Circuit Breaker", meaning the primary circuit breaker in a group or panelboard / switchboard. In IEC world, it means "Miniature Circuit Breaker", typically a DIN rail mounted circuit breaker in a small format that is limited to 100A, and is intended for use in installations with low fault current capacity (under 25kA) unless protected by upstream fuses. In NEMA world, these devices entered under special rules adopted by UL (UL1077) and are called "Supplementary Circuit Protectors" because they did not meet the criteria already established for "circuit breakers" under UL489. In recent years, many manufacturers have come out with special versions that do now meet the UL489 standards for circuit breakers, so the term MCB has taken on a dual meaning. So in NEMA world, the acronym MCB now has contextual relevance. MCBs / Supplementary Circuit Protectors are sealed units that can be neither maintained or repaired, they are throw-away devices.

MCCB Was originally an IEC term meaning Molded Case Circuit Breaker, but has been very well adopted in NEMA world now, at least at the engineering level. Many rank and file electricians still are not familiar with that acronym because its widespread use in NEMA world is fairly recent. MCCBs generally range from 15A to 1600A, with a few exceptions at either end, and generally start at 14kAIC but go up to 100kAIC for applications with high fault current capacity. There are versions that are Current Limiting (CL) as well. MCCBs are typically sealed units and cannot be serviced, although in larger sizes there are versions with interchangeable parts that can be replaced such as trip units and switch bodies.

MCP A NEMA world acronym for Motor Circuit Protector, specifically describing a magnetic-only MCCB (no thermal trip elements) that is to be used STRICTLY as part of a factory assembled, listed and tested motor starter assembly. They are often mistakenly specified and used in user-built assemblies, but this is not acceptable in the NEC (US) and CEC (Canada). In IEC world, a Motor Circuit Protector can sometimes mean a completely different device, although generally the MCP acronym is not used to avoid confusion. Devices that incorporate Short Circuit (magnetic instantaneous) trips, adjustable thermal (Overload) trips and a disconnecting means, specifically designed for motor loads, is called a Motor Circuit Protector by some manufacturers, a Motor Protective Switch (MPS) by others, a Motor Starter Protector (MSP) by others etc. etc.

ACB Short for Air Circuit Breaker, the IEC term for what is called an Insulated Case Circuit Breaker (ICCB) in NEMA world. Either term is describing a large low-voltage circuit breaker designed for high current applications up to about 6300A. ACBs typically have the facility to adjust or even disable the instantaneous trip in order to maintain protection coordination with downstream devices. The breaker is designed to be mechanically very robust in order to resist the powerful mechanical forces which exerted during fault conditions, wile waiting as long as possible for coordinated downstream devices to trip first. So essentially, an ACB/ICCB is used as almost the last line of defense during a fault. ACB/ICCBs are designed to be field maintainable, unlike MCCBs which are not.

Side note: I have seen several websites recently, particularly from China, where they use the term ACB when describing MCCBs, which is something to watch out for. This is probably a translation error on their part but is potentially dangerous if you buy an ACB from them and receive an MCCB because MCCBs are NOT designed to withstand the same kind of mechanical forces.

PCB Is short for Power Circuit Breaker, a more generic term frequently used in the past as somewhat interchangeable with ICCB when discussing Low Voltage systems, but also means large breakers in Medium Voltage systems. This was because you could have a LV Power Breaker that was either an ICCB or an ABCB, a version that used compressed air to blow out the arc when opening the breaker. ABCBs have now become the exception to the rule as ICCBs have become a lot less expensive and more reliable, so there is probably no longer a need for a generic term in LV systems. So more recently there has been concerted effort to move away from using PCB to describe Low Voltage breakers in order to help avoid confusion. But even then, the term PCB is being thrown around now as a generic Main Circuit Breaker for everything from residential load centers to electronic power supplies in appliances. So for the most part, Medium and High Voltage systems engineers are now using more specific terms depending on the design of the Power Circuit Breaker in question, i.e. Vacuum Circuit Breaker (VCB), Oil (Insulated) Circuit Breaker (OCB or OICB) or any number types of Gas Insulated Circuit Breakers (no acronym that I am aware of) such as SF6, sometimes called "Puffer Circuit Breakers".

DCB




=== Edited by tambe @ 5/2/2008 6:13 AM [GMT ] ===


Top
Thank you for this post from:
  5/14/2008, 11:42 AM
Joined 6/28/2006
Last visit: 5/19/2009
Posts: 8
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
LesPaul wrote:
hello maulik,
I want to send you a broshure with all informations you need.
But it´s to big to attach it in this reply.
Please give me an e-mail adress where I can can send it to, or contact
technical-assistance@siemens.com
regards
LesPaul


Hi Les,
It would be very nice of you if you send me those details which shows the difference between a MPCB and an MCCB.

Thanks.



=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted

Top
  3/31/2009, 4:22 PM
Joined 3/31/2009
Last visit: 5/6/2009
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Les,
It would be helpful to me if you can send the material containing the differences between MCB, MCCB & MPCB. 

Thanks,



=== Edited by O_Moderator @ 2/7/2012 10:56 AM [GMT ] ===
contact data deleted

Top
  3/31/2009, 4:44 PM
Joined 3/31/2009
Last visit: 3/2/2012
Posts: 9
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,
Other than the differences in current ratings and setting adjustments thru Pot, MCCB and MCB if thermalmagnetic, is not different and constructional principle-wise is also same.
 
MCCB with microprocessor based ETU is functionally different from MCB. Also the current adjustments cannot be done on MCB but can be done to set the Overload char of an MCCB.

MPCB characteristic is a combination of O/L relay and Circuit breaker. Its Overload characteritics is more suitable for start-up function of a motor. Where as MCCB and MCB come up with special tripping curves in order to provide that protection i.e. during motor start-up it should not have nuisance tripping. But generally MCCBs and MCBs are employed for system protection and not for Motor protection, so they do not have to have the characteristics to provide a close motor protection. Though nowadays MCCBs are with universal curves.
Top
  4/30/2009, 8:34 AM
Joined 2/7/2007
Last visit: 2/18/2013
Posts: 35
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi LesPaul,
Kindly send me a copy of the brouchure to me also.
Thanks,
Ganesan



=== Edited by O_Moderator @ 2/7/2012 10:56 AM [GMT ] ===
contact data deleted

Top
  6/30/2009, 6:29 AM
Joined 2/11/2009
Last visit: 6/1/2010
Posts: 17
Rating:
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Les,

Please send a copy of that file to me

Fahaz



=== Edited by O_Moderator @ 2/7/2012 10:56 AM [GMT ] ===
contact data deleted

Top
  8/6/2009, 4:00 PM
Joined 8/6/2009
Last visit: 8/6/2009
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi LesPaul,

Kindly send me the brouchure to me also.
Thanks,
Abdel Fateh



=== Edited by O_Moderator @ 2/7/2012 10:56 AM [GMT ] ===
contact data deleted

Top
  8/11/2009, 9:17 AM
Joined 5/27/2009
Last visit: 5/21/2013
Posts: 40
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
PLS SEND ME broshure FOR MCB, MCCB & MPCB.

thank you
ab



=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted


Nature help us, if we help Nature....
Top
  8/13/2009, 6:41 AM
Joined 7/7/2009
Last visit: 3/30/2010
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Les,

Can u please send me the Broschure too.It will be really helpfull for me.

Thanks & Regards,
Thimma Reddy.K



=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted

Top
  8/14/2009, 11:47 AM
Joined 3/5/2009
Last visit: 5/21/2013
Posts: 349
Rating:
Rated: Outstanding [3.49 out of 5 / rated 39 time(s)]. (39) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I splitted the document into two parts.
This is part1

Attachment: 002077_EN(1).pdf  (152 Downloads)

Top
Thank you for this post from:
  8/14/2009, 11:48 AM
Joined 3/5/2009
Last visit: 5/21/2013
Posts: 349
Rating:
Rated: Outstanding [3.49 out of 5 / rated 39 time(s)]. (39) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Part2

Attachment: 002077_EN(2).pdf  (132 Downloads)

Top
  10/20/2009, 2:27 PM
Joined 10/20/2009
Last visit: 10/20/2009
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi LesPaul,

Kindly send me the brouchure

Thanks, 
john



=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted

Top
  10/20/2009, 11:17 PM
Joined 8/25/2005
Last visit: 5/8/2013
Posts: 973
Rating:
Rated: Outstanding [3.68 out of 5 / rated 92 time(s)]. (92) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello JMD,

have you seen the attachments published by bilao?
Think that is what you are looking for.

Best regards
Sabine
Top
  2/6/2012, 10:12 AM
Joined 2/6/2012
Last visit: 2/6/2012
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear Les,

Could you please send me the same documents also.

regards

Amey



=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted

=== Edited by O_Moderator @ 2/7/2012 10:55 AM [GMT ] ===
contact data deleted

Top
  2/7/2012, 10:53 AM
Joined 3/5/2009
Last visit: 5/21/2013
Posts: 349
Rating:
Rated: Outstanding [3.49 out of 5 / rated 39 time(s)]. (39) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello ameyshans,
i uploaded the files to forum (just see my previous posts). Why don´t you want to download them from hereRnf:lblSmileyTooltip_  think?

Best regards
Bilao
Top
  4/4/2012, 11:27 AM
Joined 4/4/2012
Last visit: 5/18/2013
Posts: 75
Rating:
Rated: Excellent [4.56 out of 5 / rated 9 time(s)]. (9) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Sir please send a copy of that file

Thanking you.
Arun Jadhav




=== Edited by O_Moderator @ 4/4/2012 12:10 PM [GMT ] ===
contact data deleted


"Nothing is permanent, except the CHANGE"
Top
  4/4/2012, 12:12 PM
Joined 3/5/2009
Last visit: 5/21/2013
Posts: 349
Rating:
Rated: Outstanding [3.49 out of 5 / rated 39 time(s)]. (39) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
The file was uploaded here in forum by me. Just see the posts published above
Bilao wrote:
I splitted the document into two parts.
This is part1
Attachment: 002077_EN(1).pdf  (109 Downloads)

Bilao wrote:
Part2
Attachment: 002077_EN(2).pdf  (96 Downloads)
Top
  12/11/2012, 11:16 AM
Joined 7/5/2012
Last visit: 5/16/2013
Posts: 11
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
thanks for this information...
Top