Hi

Is it possible to connect MM420 ( 6SE6420-2UC23-0CA1 ) to main voltage supply 
50 HZ / 240 - 415 VAC / without any risk …???

 

Thank u…

Top
  5/17/2012, 3:05 PM
Joined 3/15/2008
Last visit: 5/20/2013
Posts: 4434
Rating:
Rated: Outstanding [3.88 out of 5 / rated 409 time(s)]. (409) 
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
6SE6420-2UC23-0CA1
MICROMASTER 420 OHNE FILTER 1/3AC200-240V +10/-10% 47-63HZ KONSTANTMOMENT  3 KW UEBERLAST  150% FUER 60S QUADRATISCHES MOMENT   3 KW 245 X 185 X 195 (H X B X T) SCHUTZART IP20 UMGEBUNGSTEMPERATUR -10+50GRD C OHNE AOP/BOP


Maximum 240 Volt!



=== Edited by IBN-Service @ 5/17/2012 3:06 PM [GMT ] ===



Industrieautomation: Softwareerstellung und Inbetriebnahme weltweit.
http://www.ibn-service.com
Top
  5/17/2012, 6:58 PM
Joined 7/8/2009
Last visit: 5/21/2013
Posts: 1167
Rating:
Rated: Excellent [4.24 out of 5 / rated 327 time(s)]. (327) 
Users with special expertise supervising conferences
Rated: Outstanding [4 out of 5 / rated 2 time(s)]. (2) 
Dhiyia wrote:

Hi

Is it possible to connect MM420 ( 6SE6420-2UC23-0CA1 ) to main voltage supply 
50 HZ / 240 - 415 VAC / without any risk …???

 

Thank u…



This drive is designed to work on 1 phase or 3phase AC but max 240V Not more than that

So 3 Phase 415V will blow your inverter

I guess IBN also said same but in German Rnf:lblSmileyTooltip_

Please say Thanks if your Problem is Solved.. :-)
Top
  5/17/2012, 8:51 PM
Joined 3/15/2008
Last visit: 5/20/2013
Posts: 4434
Rating:
Rated: Outstanding [3.88 out of 5 / rated 409 time(s)]. (409) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Vithani wrote:
...
I guess IBN also said same but in German Rnf:lblSmileyTooltip_


Maximum 240 Volt!

means

Maximum 240 Volt!

in english also.

astonished

Industrieautomation: Softwareerstellung und Inbetriebnahme weltweit.
http://www.ibn-service.com
Top
Thank you for this post from:
  5/18/2012, 7:34 AM
Joined 5/28/2008
Last visit: 5/23/2013
Posts: 2187
Rating:
Rated: Outstanding [3.65 out of 5 / rated 431 time(s)]. (431) 
Users with special expertise supervising conferences
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Dhiyia wrote:


Hi IBN-Service

Please can u re-write your post in English ... blush

Also please consider that my voltage power supply is / 50 HZ , 1 ph , 240 VAC /


Thank u...
Hello,
As IBN-Service answered in his first post, He made it Bold for you "1/3AC200-240V +10/-10% 47-63HZ". 
Numbers are the same in English & German.
In any case, here is the link of the MM420 drive. 6SE6420-2UC23-0CA1,
As adviced by friends here, You can power it uising 1/3 phase 240VAC.
For you case, power it using 1 phase, 240VAC, 50Hz. ##Attached connection diagram##
Hope this helps.

Attachment: connection.pdf  (9 Downloads)



=== Edited by Ayman Elotaify @ 5/18/2012 7:39 AM [GMT ] ===



Ayman Elotaify
MISC Egypt
www.miscegypt.com

Top
Thank you for this post from:
  5/18/2012, 7:50 AM
Joined 1/21/2012
Last visit: 3/2/2013
Posts: 46
Rating:
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 


Dear Ayman

Is there any risk as the the power supply rate will be at the max limit  240 VAC ...Rnf:lblSmileyTooltip_  think


Thank u...
Top
  5/18/2012, 8:04 AM
Joined 5/28/2008
Last visit: 5/23/2013
Posts: 2187
Rating:
Rated: Outstanding [3.65 out of 5 / rated 431 time(s)]. (431) 
Users with special expertise supervising conferences
Rated: Outstanding [3.5 out of 5 / rated 2 time(s)]. (2) 
Dhiyia wrote:


Dear Ayman

Is there any risk as the the power supply rate will be at the max limit  240 VAC ...Rnf:lblSmileyTooltip_  think


Thank u...
Hello 
No. There will not any risk. The limitation is as follows: "AC200-240V +10/-10% 47-63HZ"
With best regards.

Ayman Elotaify
MISC Egypt
www.miscegypt.com
Top
Thank you for this post from:
  5/18/2012, 9:39 AM
Joined 4/21/2006
Last visit: 5/22/2013
Posts: 312
Rating:
Rated: Outstanding [3.3 out of 5 / rated 20 time(s)]. (20) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I deleted the non-technical postings.