Hello,
The task of connecting the emulator of the SSI probe FM458. RS485 of emulator provides an output voltage with the difference only 2 volts.
After connecting to the M458 on the line with the data appears offset from zero, which causes the logic 0 corresponds to 0 volts and a logic 1 corresponds to 2 volts. How do I get when connecting the FM ± 1 volt?

http://www.wiki-kollmorgen.eu/wiki/DanMoBilder/file/pdf_archiv/drives_AC_digital/SERVOSTAR/SR300/2011-09/sr300_e.pdf

This is a reference to the description of servoamplifier, which emulates the SSI encoder. On page 86 a description of the encoder emulation.

Thanks.
Top
  5/16/2012, 9:08 AM
Joined 8/25/2006
Last visit: 5/20/2013
Posts: 898
Rating:
Rated: Excellent [4.2 out of 5 / rated 85 time(s)]. (85) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello.
Did you try to connect your emulator to the EXM438 and read its data in CFC at block AENC?
RS-485 regulates only difference between DATA+ and DATA- voltages of encoder, that must be >200mV for 1 and <-200mV for 0.
But note that EXM438 supports only 13 or 25 bit encoders +parity.
Top
Thank you for this post from:
  5/17/2012, 4:53 PM
Joined 5/15/2012
Last visit: 5/17/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thank you for reply. The problem was solved by replacing the RS485 chip on the same.
topic can be closed.
Top
  8/16/2012, 6:08 AM
Joined 5/14/2008
Last visit: 5/10/2013
Posts: 18
Rating:
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
KSN wrote:
Hello.
Did you try to connect your emulator to the EXM438 and read its data in CFC at block AENC?
RS-485 regulates only difference between DATA+ and DATA- voltages of encoder, that must be >200mV for 1 and <-200mV for 0.
But note that EXM438 supports only 13 or 25 bit encoders +parity.


Dear KSN i have used 24bit encoder + parity with EXM438 and it works fine. EXM438 accepts 13 to 25 bit encoder but in help file of AENC block it is clearly mentioned 13 or 25 bit encoders.