Hello Experts,
Drive MLFB no is 6RA7025-6DV62. Drive shows fault A035. What could be the reason?
Thanks in advance.

DEEP.

Tell me and I will forget. Show me and I will remember. Involve me and I will understand. -Confucius
Top
  5/3/2012, 11:54 AM
Joined 8/25/2006
Last visit: 6/18/2013
Posts: 909
Rating:
Rated: Excellent [4.21 out of 5 / rated 86 time(s)]. (86) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello.
Look at the manual, description of fault F035 and check the parameter P355, if it is 0, then instead of fault F035 alarm A035 activated.

Following conditions are fulfilled for longer than the period set in parameter P355:

♦  Positive or negative torque or armature current limit 
♦  The armature current is higher than 1% of the converter rated armature DC current 
♦  The actual speed is less than 0.4% of maximum speed 
 
Possible fault causes 
♦  Drive is blocked