hello,
i use operator panel mp377and i want to  put limit value(0-20) to io field object. how can i do it?

J.SANCHEZ
Top
  5/3/2012, 10:09 AM
Joined 8/27/2006
Last visit: 6/18/2013
Posts: 259
Rating:
Rated: Outstanding [3.14 out of 5 / rated 22 time(s)]. (22) 
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
you can put a limit value to a tag, not to a field object.
Select your required tag, right click, properties and set the limit for that tag.

The more you know, The more you know you don't know
Top
Thank you for this post from:
  5/3/2012, 1:13 PM
Joined 12/27/2007
Last visit: 5/23/2013
Posts: 251
Rating:
Rated: Very Good [2 out of 5 / rated 4 time(s)]. (4) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
if you want to see the limit od the tag as a tooltext in RT then you have to enable the settings in HMI setting

Regards,
Prats
Top
  5/5/2012, 8:44 AM
Joined 8/4/2010
Last visit: 6/11/2013
Posts: 118
Rating:
Rated: Excellent [5 out of 5 / rated 2 time(s)]. (2) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
thank you so much 



J.SANCHEZ
Top