Hi,
I am not able to open wincc. I am getting the following error " User does not have the rights to perform this action. Please check the assignment of the current user". Same i attached here...

In the same system i can able to open the wincc in administrator login.
What may be the problem and what i need to check??? 

Attachment: error.zip  (7 Downloads)

Top
  4/18/2012, 8:08 AM
Joined 4/22/2010
Last visit: 5/25/2013
Posts: 3216
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

In Windows user administration give that user administrator rights.

What O.S. you have there?

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top
  4/25/2012, 6:53 AM
Joined 3/24/2009
Last visit: 4/25/2013
Posts: 335
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi, 
Thanks for your reply..
I am using Windows XP...
I tried by applying rights for the user but still the problem remains same....
Top
  4/25/2012, 7:23 AM
Joined 10/3/2010
Last visit: 5/23/2013
Posts: 732
Rating:
Rated: Outstanding [3.39 out of 5 / rated 49 time(s)]. (49) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Please be more specific about your problem.

Which version of WinCC + SP/Updates are you using?
Are you trying to open the WinCC project on the WinCC PC itself or through a network on a client PC?
Is it a copy of an existing project or a project created on that PC?
Do you have more than 1 ethernet card in your PC?

Maybe this can help:
http://support.automation.siemens.com/WW/view/en/19346272

Did you try to duplicate this project?

Did you try to duplicate this project under another name on the PC and check if that one opens? Use Project Duplicator and change project name and directory. Open the new changed project.
If you can open the duplicated project, close it again and delete the old project (keep a backup somewhere) and duplicate the working one again with the original project name.


brgds



=== Edited by SteBo @ 4/25/2012 7:37 AM [GMT ] ===


Top
  4/25/2012, 9:04 AM
Joined 8/27/2006
Last visit: 5/14/2013
Posts: 259
Rating:
Rated: Outstanding [3.14 out of 5 / rated 22 time(s)]. (22) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I had this problem last month. My mistake was that I had many PCs and I needed the same SCADA on each PC, so I cpoied/pasted the project. This caused WinCC to give me the user rights message.
The solution for this problem is to use the project duplicator found in Start->Programs->Simatic->WinCC->Tool->Project Duplicator
This will create a project saved on your local drive (not that you can't save directly on a networked PC or on a Flash drive)
You should take that project and copy it to the other PC.
When you open the WinCC project from WinCC expolrer, you should select to start the project locally and the you have to change the PC name and system parameters.

The more you know, The more you know you don't know
Top
  4/25/2012, 9:50 AM
Joined 1/17/2007
Last visit: 4/23/2013
Posts: 131
Rating:
Rated: Excellent [4.75 out of 5 / rated 4 time(s)]. (4) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Samkcr

I had the exact same problem a few days ago.
Check out my tip page https://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?HTTPS=REDIR&PostID=360723&language=en

There is a pdf document with screenshots of the problem and the resolution.

When I tried to open the WinCC project on the client after downloading I got the exact same message.

Good luck and I hope your problem gets solved.
Top
  4/25/2012, 10:12 AM
Joined 10/3/2010
Last visit: 5/23/2013
Posts: 732
Rating:
Rated: Outstanding [3.39 out of 5 / rated 49 time(s)]. (49) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Bilal Moolla wrote:
Hi Samkcr

I had the exact same problem a few days ago.
Check out my tip page https://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?HTTPS=REDIR&PostID=360723&language=en

There is a pdf document with screenshots of the problem and the resolution.

When I tried to open the WinCC project on the client after downloading I got the exact same message.

Good luck and I hope your problem gets solved.


Thanks for this pdf, probably not the same situation but one might get some clues from it.
Using Project Duplicator instead of copy/paste a WinCC project, every necessary share should be create automatically. It often solves issues like this.