Dear Collegues
I would like to know if "BU2" in Simocode "pro V"  directly accepts 110 Vac inputs or necessary include "DM" expansion for that?.
Thank ypu so much in advance
Top
  4/5/2012, 12:01 PM
Joined 12/9/2011
Last visit: 4/12/2013
Posts: 10
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

SIMOCDOE Pro BU1 or BU2  both accept inputs only at 24 V DC internally generated. The 110VAC from field has to be connected to an interposing relay for the same before connecting to DIs. alternatively you can connect 110 VAC directly to DM in BU2.
Hope it helps.
regards,
Harshwm