Since about 2 weeks ago
one of our cpu's crushed and all front led's start blinking
therefor we replaced it with new one and now another one failed! with same problem!
can any one help me why these problem happen for our system and give me more information to prevent these problem?!
thx&sorry for my bad englishblink
Top
  11/11/2011, 10:47 AM
Joined 4/22/2010
Last visit: 6/18/2013
Posts: 3307
Rating:
Rated: Excellent [4.12 out of 5 / rated 300 time(s)]. (300) 
Users with special expertise supervising conferences
Rated: Outstanding [4 out of 5 / rated 1 time(s)]. (1) 
Hello,

2 cpu's dead in a short time can be a lot of things:

1. Cpu really defect, check power supply, memorycard if there and possible EMC problems.
2. Cpu is o.k. but there is a problem with the backplane.

So check the cpu in another rack with another powersupply unit and have a good look at grounding/ shielding of cables and other equipment in the cabinet.

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!
Top
Thank you for this post from:
  11/11/2011, 4:20 PM
Joined 8/5/2008
Last visit: 3/22/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear sir
thank for u'r attention
I've check defect CPU in another Rack with new power supply
It works some times! ( another time all LED's blink! or INTF&EXTF blinking (with out stop LED) or all front LED's are ON) if I update firmware what will happen to CPU's(work or not)
and about grounding and schielding I'm sure about them(check it before)
and main powers are comming from UPS
also i must remember I've install new cpu's on old backplaine but work correctly without error
and also these 2 cpu's are for two defrent department but in a one electrical room(rawmill&kiln-CEMENT INDUSTRY-)
thank's
Top
  11/17/2011, 8:43 AM
Joined 10/31/2005
Last visit: 6/13/2013
Posts: 2107
Rating:
Rated: Excellent [4.08 out of 5 / rated 200 time(s)]. (200) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
      Check your old (replaced) CPU with new backplane. I guess problem is in rack. Also can check current backplane for broken pins - improper installing of module can cause pins to be bound - can be a problem. MMC can also be a problem, as Marсофт mentioned - can you run PLC without it (as you have UPS it seems you wont have problems with power, so removing MMC can be regarded as normal).  