PedroB wrote:
i am working with help example with 3 participants and 1 61850 station and I can declare the origins but I didn't declare the destinations since neither in the window of destinations neither in the main menu the buttom destinations it is not enabled, neither too I can drag and drop the destination to the linking window like I make with the origin, i can´t see DO attributes in the destination window...

best regard
Top
  11/17/2011, 4:43 PM
Joined 10/9/2007
Last visit: 6/19/2013
Posts: 563
Rating:
Rated: Outstanding [3.62 out of 5 / rated 45 time(s)]. (45) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi

Send some pictures.


Mike

Energy Automation products: Sicam, Siprotec, Digsi
Top
  11/17/2011, 5:02 PM
Joined 11/10/2011
Last visit: 11/21/2011
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi, like you see DO attributes not deployed in destiny window

thanks for your help

PedroB

Attachment: digsi configurator.JPG  (34 Downloads)

Top
  11/17/2011, 5:12 PM
Joined 10/9/2007
Last visit: 6/19/2013
Posts: 563
Rating:
Rated: Outstanding [3.62 out of 5 / rated 45 time(s)]. (45) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi

Are you the same who made this question here?
https://www.automation.siemens.com/WW/forum/guests/PostShow.aspx?PageIndex=1&PostID=322318&Language=en&onlyInternet=False#top

The same answer apply:
 did you configure one of the Siprotecs to receive GOOSE Messages?
You should have some "External Information" and as source the column S (system) activate.


Mike

Energy Automation products: Sicam, Siprotec, Digsi
Top
  11/17/2011, 10:32 PM
Joined 11/10/2011
Last visit: 11/21/2011
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thank you, problem is solved, i was using EM instead of  ExAS like i had read in a help in spanish,
for my all well,
thank you again 
PedroB
Top
  11/18/2011, 9:29 AM
Joined 10/9/2007
Last visit: 6/19/2013
Posts: 563
Rating:
Rated: Outstanding [3.62 out of 5 / rated 45 time(s)]. (45) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi

Thanks for the Feedback

These information starting with Ex... are the External information.



Mike

Energy Automation products: Sicam, Siprotec, Digsi
Top