Dear Experts,

We’re encountering some strange warnings when we compile our WinCC project (sometimes up to 4212 warnings). Even after reorganizing the project in Simatic Manager, delete the temporary files in WinCC, using “Save and Optimize” in WinCC and rebuild the complete project again the (blue) warnings remain.
Underneath you will find the warnings we get:

-          Warning:  The STEP7 text lexicon ERRTEXTLIBEXPNddd43540-820b-4150-8db5-574a5f5c25a2 for the alarm-s message 1610612756 in value 3 was not found.

-          Warning:  The number of values in the STEP 7 ALARM_S alarm 1610612743 'nl-NL' exceeds the maximum number.

Does anyone encounter the same problems? Does anyone know a suitable solution to avoid this annoying warnings? Thanks in advance!

We’re using Simatic WinCC flexible version 2008 SP2 Upd13 and Simatic Manager version V5.5 + SP1.

As far as I’m aware these warnings did appear after the last update of Simatic Manager.

Thanks in advance for all your help.

Attachment: Problem WCC-Flex.jpg  (40 Downloads)

Top
  10/25/2011, 3:39 PM
Joined 9/5/2011
Last visit: 5/23/2013
Posts: 2587
Rating:
Rated: Outstanding [3.83 out of 5 / rated 132 time(s)]. (132) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

You should copy from Step 7 the WinCC flexible project with the function " Copy from Step7".
You find this function in WinCC flexible, Project --> Copy from Step7.
Then you open this WinCC flexible Project(standalone).
You use the function  "Delete Temporary Files". Options ---> "Delete Temporary Files"
You use the function " Rebuild All". Project -->Compiler --> Rebuild All
You save the project and use for integration of the project the function "Integrate in Step7".
 
Tweety



=== Edited by Tweety @ 10/25/2011 3:41 PM [GMT ] ===


Top
  10/25/2011, 4:28 PM
Joined 10/25/2011
Last visit: 1/21/2012
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Tweety,

Thanks for your prompt reply! I just followed the steps you mentioned, but unfortunately without any luck (please see attachment for a screenshot). Both errors remain (sometimes I get more, sometimes I get a couple less). I hope you have more ideas in order to solve this problem.

Thanks in advance for all ideas!

Attachment: Problem WCC-Flex v2.jpg  (39 Downloads)

Top
  10/26/2011, 9:28 AM
Joined 9/5/2011
Last visit: 5/23/2013
Posts: 2587
Rating:
Rated: Outstanding [3.83 out of 5 / rated 132 time(s)]. (132) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

you can contact the customer support for your behaviour.
Perhaps the support can repair the project.
Customer Support

Tweety



=== Edited by Tweety @ 10/26/2011 10:46 AM [GMT ] ===


=== Edited by Tweety @ 10/26/2011 9:38 AM [GMT ] ===


Top
  10/26/2011, 10:45 AM
Joined 10/25/2011
Last visit: 1/21/2012
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks! I will do.
Top
  12/5/2011, 11:20 PM
Joined 1/27/2010
Last visit: 5/25/2012
Posts: 7
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Expert_engineer,

Did you find a solution to this problem?? I have the same thing happening!

Regards,

Jay
Top
  12/7/2011, 9:19 AM
Joined 4/29/2010
Last visit: 4/4/2013
Posts: 1363
Rating:
Rated: Outstanding [3.67 out of 5 / rated 125 time(s)]. (125) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Jay,

do you allready try the mentioned steps they talk about in this thread?

best regardsRnf:lblSmileyTooltip_sheep
Top
  12/9/2011, 6:32 AM
Joined 1/27/2010
Last visit: 5/25/2012
Posts: 7
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Yes i have, but to no avail.

I haven't contacted support yet, they never seem to be of much use anyway, which is why I was trying around on the forums.
Top
  12/12/2011, 3:15 PM
Joined 9/5/2011
Last visit: 5/23/2013
Posts: 2587
Rating:
Rated: Outstanding [3.83 out of 5 / rated 132 time(s)]. (132) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello
Tweety wrote:
Hello,

You should copy from Step 7 the WinCC flexible project with the function " Copy from Step7".
You find this function in WinCC flexible, Project --> Copy from Step7.
Then you open this WinCC flexible Project(standalone).
You use the function  "Delete Temporary Files". Options ---> "Delete Temporary Files"
You use the function " Rebuild All". Project -->Compiler --> Rebuild All
You save the project and use for integration of the project the function "Integrate in Step7".
 
Tweety

You do this with your project?
Then you can try this.
You delete the FB 44, FB 45 and DB 44, DB 45 in your S7 project. This are the default FBs and DBs.Then you must generate the alarm S messages in S7 PDIAG new.
Tweety
Top
  12/13/2011, 11:58 PM
Joined 1/27/2010
Last visit: 5/25/2012
Posts: 7
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Yes tweety, I tried all of these, but nothing seems to work.

It doesn't stop the project from functioning, but it is quite annoying! It would be nice to compile with no warnings.
Top
  12/14/2011, 3:17 PM
Joined 9/5/2011
Last visit: 5/23/2013
Posts: 2587
Rating:
Rated: Outstanding [3.83 out of 5 / rated 132 time(s)]. (132) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

If this does not help, you can contact the customer support for your behaviour.
Perhaps the support can repair the project.
Customer Support


Tweety
Top
  1/18/2012, 3:38 PM
Joined 1/18/2012
Last visit: 1/31/2012
Posts: 1
Rating:
Rated: Excellent [5 out of 5 / rated 2 time(s)]. (2) 
Rated: Excellent [5 out of 5 / rated 2 time(s)]. (2) 
Hi,

had the same problem after I installed Step7 v5.5 SP1.

Got the following solution from Siemens support:

1. Open the HW Config of the PLC select the PLC and go to \Options\Report system error\"Messages and remove the flag "Optimized creation of messages".
2. Open your WinCC Flexible project and try again.

If this doesn´t help Please do the following:
1. Open your WinCC Flexible project and "copy from Step 7" under /Project/copy from Step 7.
2. Open your Step 7 project an delete the old WinCC Flexible projekct.
3. Deleting the instanz DB´s.
4. Please save the project with the function "save as" and pick the option "With reorganization (slow)" .
5. Open the WinCC flexible project.
6. In WinCC Flexible please open "Project/Integrate in STEP7 and select your new Step 7 project.
7. then create in Step 7 (Netpro) a new connection from HMI to PLC and try again.


Regards
Rikard



=== Edited by Rikard_sweden @ 1/18/2012 3:41 PM [GMT ] ===


Top
Thank you for this post from:
  1/21/2012, 8:03 AM
Joined 10/25/2011
Last visit: 1/21/2012
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I've got the same thing from support. But it doesn't seems to work. Did it do the trick with your project?
Top
  1/23/2012, 10:47 AM
Joined 9/5/2011
Last visit: 5/23/2013
Posts: 2587
Rating:
Rated: Outstanding [3.83 out of 5 / rated 132 time(s)]. (132) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Tweety wrote:
Hello
You do this with your project?
Then you can try this.
You delete the FB 44, FB 45 and DB 44, DB 45 in your S7 project. This are the default FBs and DBs.Then you must generate the alarm S messages in S7 PDIAG new.
Tweety


Do you have try already this?

Tweety
Top
  3/30/2012, 2:02 PM
Joined 8/10/2006
Last visit: 5/23/2013
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rikard_sweden wrote:
Hi,

had the same problem after I installed Step7 v5.5 SP1.

Got the following solution from Siemens support:

1. Open the HW Config of the PLC select the PLC and go to \Options\Report system error\"Messages and remove the flag "Optimized creation of messages".
2. Open your WinCC Flexible project and try again.


Regards
Rikard

 
Hi Rikard.

This problem is solved with the above first idea.

My program is Step7 v5.5 SP1 and WinccFlexible 2008 SP2. How to run other functions, this method will have an effect?

Thank you...
Top
  4/2/2012, 11:03 AM
Joined 9/5/2011
Last visit: 5/23/2013
Posts: 2587
Rating:
Rated: Outstanding [3.83 out of 5 / rated 132 time(s)]. (132) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
sekoco wrote:
 
Hi Rikard.

This problem is solved with the above first idea.

My program is Step7 v5.5 SP1 and WinccFlexible 2008 SP2. How to run other functions, this method will have an effect?

Thank you...


Hello sekoco,

Can you say more about your behaviour which you have with Step7 and WinCC flexible?
Can you post a screenshot about this?

Tweety
Top
  4/3/2012, 9:13 AM
Joined 8/10/2006
Last visit: 5/23/2013
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Tweety wrote:
sekoco wrote:
 
Hi Rikard.

This problem is solved with the above first idea.

My program is Step7 v5.5 SP1 and WinccFlexible 2008 SP2. How to run other functions, this method will have an effect?

Thank you...


Hello sekoco,

Can you say more about your behaviour which you have with Step7 and WinCC flexible?
Can you post a screenshot about this?

Tweety


Hi Rikard. Thank you for your reply.

This solution replaces something else? I had asked...

Do not have another problem. This problem is solved.

Thanks.