Hello to everyones,
do you know what happens if a PLC slave (CPU314C-2DP) with OB122, loses the communication with the master?
If the PLC slave receives some setpoints of regulation from the master, after the loss of communication the slave keeps on commanding his out with the same values of setpoint?

Thanks in advance
Top
  3/13/2011, 4:19 PM
Joined 12/22/2006
Last visit: 5/18/2013
Posts: 1295
Rating:
Rated: Excellent [4.01 out of 5 / rated 151 time(s)]. (151) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,
Because the CPU314 is a programmable device, the application can be written to react the way you want when the master is not reachable.
Of course the input range filled up by the master is filled with "0" when the master is missing.
But the loss of communication with the master can be detected (OB86 is called).

Best regards
jklm

Suggestion was helpful? Thanks to rate it.
Top
  3/14/2011, 5:27 PM
Joined 9/1/2010
Last visit: 4/3/2013
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks for your explanation!