hello,
Please look at the manual of Simocode Pro on page 3-11.
Type of Load
You can select whether SIMOCODE pro is to protect a 1-phase or a 3-phase
load.
For a "1-phase" Type of Load, proceed as follows:
• The Internal Earth-fault Monitoring and the Unbalance Protection must be
deactivated
• Only one of the two cables is to be fed through any through-hole opening in
the Current Measuring Module.
Phase Failure Monitoring is deactivated automatically.
kind regards