Connection problem S5 with Lauer HMI

Thread Starter: Spud2408   Started: 8/27/2008 5:02 PM   Replies: 7

« Previous thread Next thread »
Page 1 of 1 (8 items)
  8/27/2008, 5:02 PM
Joined 8/7/2008
Last visit: 8/30/2008
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi
I have  problem. I have the old system with S5 115U CPU 943 (with 2 TTY) which is connected with HMI Lauer PCS090 on TTY2 and it is working perfect.
Now I`m making new same maschine whith same system, HMI Lauer which is connected with S5 115U CPU 943 B (with 1 TTY), I upload  the same program to  CPU and  to HMI, only difference is that HMI is now connected to TTY 1 (becouse this CPU has only 1 TTY) could this be a reason why  HMI is showing:                           -connection  error-
                                           -wrong DB-


What is the difference between CPU 943(with 2 TTY)  and 943B (with 1)?

Thanks
Top
  8/27/2008, 7:18 PM
Joined 8/17/2007
Last visit: 10/3/2013
Posts: 488
Rating:
Rated: Excellent [4.29 out of 5 / rated 34 time(s)]. (34) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
In the single serial interface, the interface port uses AS511 protocol for communication using TTY signals. If there is a second interface, the SI2 (second serial interface) of the CPU could be configured to communicate in different protocols such as point-to-point, ASCII, 3964R etc.
May be your HMI is using some protocol other than AS511.

Did you try connecting new HMI on the old CPU?

Jomy M Jose
Jacobs Engineering Group Inc.
111 Corning Rd., Suite 200
Cary, NC 27518, USA
Top
  8/27/2008, 7:25 PM
Joined 8/17/2007
Last visit: 10/3/2013
Posts: 488
Rating:
Rated: Excellent [4.29 out of 5 / rated 34 time(s)]. (34) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Also check this manual if you need more info

http://support.automation.siemens.com/WW/view/en/1085937

Jomy M Jose
Jacobs Engineering Group Inc.
111 Corning Rd., Suite 200
Cary, NC 27518, USA
Top
  8/28/2008, 8:32 AM
Joined 8/7/2008
Last visit: 8/30/2008
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi JMJ,
  thanks for  answer.
Thing is that we have on stock only this CPU.
But normali S5 program that I put on this CPU with one SI is made for CPU with two SI and I think that  protocol for this HMI is also AS511.
I don t know what to do if problem is in CPU it is not a problem to buy a new.
Top
  8/28/2008, 11:19 AM
Joined 4/24/2006
Last visit: 9/16/2014
Posts: 5571
Rating:
Rated: Excellent [4.19 out of 5 / rated 532 time(s)]. (532) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Spud2408,

Please check you S5 programm. Is it using FB51 (TDOP511) then it is AS511 protocol
or is it using FB53 (FAP protocol, only SI2 interface)?

Best regards,

Wizard
Top
  8/28/2008, 4:37 PM
Joined 8/7/2008
Last visit: 8/30/2008
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Wizard,

                  it is using FB50, does this means anything?
Top
  8/28/2008, 6:28 PM
Joined 8/17/2007
Last visit: 10/3/2013
Posts: 488
Rating:
Rated: Excellent [4.29 out of 5 / rated 34 time(s)]. (34) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
As per my knowledge these are the blocks for TDOP communication for S5

 

ConnectionFB No.FB Name
AS511FB51TDOP:511
FAP to SI2FB53TDOP:FAP
FAP via CP521 SIFB52TDOP:521
FAP via CP523FB52TDOP:523
PROFIBUS-DPFB58TDOP:DP
SINEC L1FB56TDOP:L1
PROFIBUSFB55TDOP:L2
ParallelFB54TDOP:PAR

Now, I do not know what FB50 is, what is the FB name?

Jomy M Jose
Jacobs Engineering Group Inc.
111 Corning Rd., Suite 200
Cary, NC 27518, USA
Top
  8/28/2008, 6:48 PM
Joined 8/17/2007
Last visit: 10/3/2013
Posts: 488
Rating:
Rated: Excellent [4.29 out of 5 / rated 34 time(s)]. (34) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I find at Lauer site that tey have comm manual for PCS with S5 but it is in German. I do not undestand much German, but it look like they have their own blocks for communication.

http://www.lauer-systeme.net/web/lauer_en.nsf/AllDocuments/56C0956211F4317AC1257380002FD9BD


http://ft.beijer.se/files/C12572A600329472/972EAF32BD285600C125740100547693/91SIE_D.PDF

May be someone who understands German can help.

Jomy M Jose
Jacobs Engineering Group Inc.
111 Corning Rd., Suite 200
Cary, NC 27518, USA
Top