Technical Forum

SINUMERIK CNC automation systems

Simodrive 611 Error Code

Thread Starter: the_cnc_guy   Started: 10/16/2013 5:26 PM   Replies: 1

« Previous thread Next thread »
Page 1 of 1 (2 items)
  10/16/2013, 5:26 PM
Joined 6/20/2013
Last visit: 10/16/2013
Posts: 6
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
We have a CNC lathe with a simodrive 611 ( 6sn1123-1ab00-0ca3 ). We cant enable the system due to an error on the simodrive.

E ( then 3 horz lines ) B607 is on the drives LCD display. Cant find the siemens doc for this drive. Need to know what this alarm is so I can remedy the alarm.

TIA,
the_cnc_guy



=== Edited by the_cnc_guy @ 10/16/2013 5:27 PM [GMT ] ===


Top
  10/16/2013, 5:44 PM
Joined 1/29/2008
Last visit: 12/15/2014
Posts: 414
Rating:
Rated: Outstanding [3.17 out of 5 / rated 18 time(s)]. (18) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi
The error means:
607 Current controller output limited
Cause The entered setpoint cannot be impressed in the motor, although the
maximum voltage has been entered. The cause could be that the motor
is not connected, or a phase is missing.
Remedy -- Check the connecting cable, motor/drive converter (phase missing)
-- Check the motor contactor
-- DC link voltage present?
-- Check the DC link busbar (check that the screws are tight)
-- Uce monitoring function in the power section has responded
(RESET by powering off/powering on)
-- Replace the power section or control module
Good luck
Nit