hello !

I had a problem with a MM440 which is not starting and tripping directly. I thought maybe the drive was the problem so i changed it by a same rating. It happens the same.
I try to run the drive from PC (drive monitor). In the error list i see the code 453.
I disconnect output cable and still tripping from the same fault. Drive was in operation before i put it.

Anyone can help on this. I think from the code that is the error F0453 which i do not see on the fault list of MM440. I read other threads telling that this is the code error for Motor stall but normally i have run other times Inverters without output cable connected and normally it will run only having A0922 which means no load applied to the inverter.
Drive type is 6SE6440-2UD31-5DA1

Anyone can help on this please !
Top
  9/9/2013, 9:37 AM
Joined 1/21/2013
Last visit: 7/24/2014
Posts: 1505
Rating:
Rated: Outstanding [3.94 out of 5 / rated 71 time(s)]. (71) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi
you've already seen this thread?
Fault F0453 - Siemens Industry Online Support - Technical Forum ...
Top
  9/9/2013, 10:57 AM
Joined 7/2/2010
Last visit: 6/17/2014
Posts: 21
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Yes i have already look at this thread but i do not think is my case because i do not any motor connected to the drive. 
Top
  9/11/2013, 9:27 AM
Joined 7/8/2009
Last visit: 7/24/2014
Posts: 1851
Rating:
Rated: Excellent [4.18 out of 5 / rated 447 time(s)]. (447) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

What is the control mode you using? I think for vector control (with or without sensor), you need to run motor. Try setting control mode to V/F scalor mode and try to run drive without motor.

You said you cant find F453 in fault list

Please check updated Manual. You will find it in the list Rnf:lblSmileyTooltip_

Parameter List: MICROMASTER 440

Regards,
Devesh


I dont Like people driving Fast, thats the reason I overtake them ;)
Top
  9/11/2013, 2:14 PM
Joined 7/2/2010
Last visit: 6/17/2014
Posts: 21
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello !

Thank you for your help !

I also think it is the control mode which makes this problem.
The same inverter is working perfectly for a water pump application P1300 = 0.

I took this inverter to use it for a vibrating feeder which have to motors of 4 Kw each one.

Now i put the same parameters of the inverter which was installed before that is damaged.
In this case P1300 = 20

What do u suggest ?

Thank you very much for your help !
Top
  9/12/2013, 12:04 PM
Joined 7/2/2010
Last visit: 6/17/2014
Posts: 21
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello !

This problem was solved !

I learned from the manual that in cases when is used the control mode sensorless vector control P1300=20 it is very important to carry out the motor data identification from the inverter P1910.

After doing this the inverter started without any problem !

Thank you for the support !