Hi
I have project with I/O module Cube 67+ (Murrelektronik). My PLC is S71200 CPU 1215. I can´t found libraries for TIA portal. I don´t know about faults on module Cube 67+.
Please help me.
Thanks. MartinRnf:lblSmileyTooltip_  
Top
  11/26/2012, 3:04 PM
Joined 7/7/2010
Last visit: 9/23/2014
Posts: 3213
Rating:
Rated: Outstanding [4 out of 5 / rated 362 time(s)]. (362) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
mdvorscak70 wrote:
Hi
I have project with I/O module Cube 67+ (Murrelektronik). My PLC is S71200 CPU 1215. I can´t found libraries for TIA portal. I don´t know about faults on module Cube 67+.
Please help me.
Thanks. MartinRnf:lblSmileyTooltip_  

You are looking for library for a non-Siemens product on a Siemens forum?  What is this cube?  How does it communicate?  Profinet?  Can you use standard profibus/profinet diagnostics according to the closed documentation available on the profinet/profibus standards web site (pay to access documentation for the supposedly open standard??)?

Helpful? Rate it.
Solved? Post it.
http://geo.co/s/EyRK
Top
  11/26/2012, 5:01 PM
Joined 9/27/2006
Last visit: 9/23/2014
Posts: 4794
Rating:
Rated: Excellent [4.21 out of 5 / rated 819 time(s)]. (819) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Martin;
Huggy is right, the responsability of providing software intefraces and operationg manuals for a Profibus-DP slave is on the manufacturer of the product.
On this page from Murr elektronic you will find what is needed for your application:
https://onlineshop.murrelektronik.com/mediandoweb/index.php?ID_O_PRODUCT=78693&ID_O_TREE_GROUP=135&BEGIN=1&sLanguage=English&pageturning=10

You will first have access to the gsd file required to integrate the Cube67 Porfibus slave in the Profibus configuration of the master; then you can find the operating manual for this profibus slave, and finally you have a sample project for integration to a DPV1 master.
The CM 1243-5 is the DPV1 Profibus-DP master module you would need to connect your CPU 1215 to profibus.
SIMATIC NET S7-1200 - PROFIBUS CM 1243-5  

Hope this helps,
Daniel Chartier



=== Edited by dchartier @ 11/26/2012 5:07 PM [GMT ] ===


Top
  12/6/2012, 11:43 AM
Joined 7/7/2009
Last visit: 9/2/2014
Posts: 2
Rating:
Rated: Outstanding [4 out of 5 / rated 1 time(s)]. (1) 
Rated: Outstanding [4 out of 5 / rated 1 time(s)]. (1) 

Hi!

As far as I know you shouldn’t need any library to read diagnostics from a Profibus Slave or a Profinet Device. Reading the TIA Portal Help you will find functions (DPNRM_DIAG or GET_DIAG, for example) that should retrieve the diagnostic information that was sent from the slave/device from the Profibus Master or Profinet Controller into your application program.

Sadly we found out that these functions are still not working as they should. As soon as a third party slave/device generates a diagnostic (we tested with Murrelektronik and other products) the S7-1200 will indicate that. But as soon as the diagnostic is gone the S7-1200 won’t reset the diagnostic state and will stay forever in this state.

We contacted Siemens in Germany and informed about that. The original support case (SR-Number 1-2777626655 from 2012-05-25 13:51) was passed to Development (SR-Number 1-2816495278 from 2012-06-05 11:35) and on 2012-07-05 15:20 we received following answer:

“Wir haben die Mitteilung von unserer Entwicklung bekommen, dass sie bemüht ist, dass von Ihnen geschilderte Verhalten zum Update 5 der Version V11.0 des TIA Portals zu verändern. Das Erscheinungsdatum dieser Version ist uns noch nicht bekannt, aber wir werden Sie informieren, sobald diese Version zum Download oder zur Bestellung bereit steht.”

what means (optimized Google translation)

We received the notification from our development that they are doing all the efforts to change the behavior you described for Update 5 version of the TIA Portal V11.0The release date of this version is still unknown, but we will inform you as soon as this version is ready for download or order.

And we are still waiting...

With S7-300 and S7-400 Series there are no problems.

By the way, there is no need to order any documentation from the PNO Site. The standards only specify how Slave/Device and Master/Controller exchange diagnostic information. How you retrieve this information from the Master/Controller into your application program isn’t specified because this is an internal interface between the Master/Controller and the “PLC”. In this case you should always read the PLC documentation.

And the DP-V1 function block that dchartier mentioned isn’t for diagnostic purposes but for acyclic data exchange between your application and the Cube67+ Station (to turn the branchs on and off to change the configuration of the Station – very useful when you have a machine with options where not all modules are connected, for example).

In case you need more information, please do contact Murrelektronik Support directly in the US or in Germany.