MP277 10" Touch is not starting after Power ON

Thread Starter: 007   Started: 2/9/2012 8:52 AM   Replies: 7

« Previous thread Next thread »
Page 1 of 1 (8 items)
  2/9/2012, 8:52 AM
Joined 11/29/2007
Last visit: 9/18/2014
Posts: 34
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear All,

After Power ON to MP277 10" touch HMI, following display on screen

Step wise-

1) Reporting

   MP277-10 touch

   version1:1

2) Formatting winCE flash  system partiton no-0

wait.....done

3) Scanning winCE partition no-1

wait....done

4) Scanning winCE flash file system partition no -1

wait...done

startup in progress

Point 4th is continuously shown in hmi and no control panel display on screen.


plz suggest


Regards,
Rajesh

Top
  2/9/2012, 8:54 AM
Joined 9/28/2005
Last visit: 7/4/2014
Posts: 2927
Rating:
Rated: Excellent [4.03 out of 5 / rated 214 time(s)]. (214) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

You need to reflash the panel with the option 'Reset to factory defaults'. In that case ProSave will catch panel's bootloader and start to reflash panel at that point. It should help you 90% blink. Please read manual of MP277 on how to do it. SIMATIC HMI HMI device MP 277 (WinCC flexible) chapter 7.7.2. Also here What settings do you have to make on an MP 377 to reset the operator panel to the factory settings?. MP is different, but procedure is the same.



=== Edited by Darius @ 2/9/2012 9:02 AM [GMT ] ===


=== Edited by Darius @ 2/9/2012 9:00 AM [GMT ] ===



Regards,
--------------------------------
Darius
Automation engineer/programmer
Top
  2/9/2012, 10:30 AM
Joined 12/13/2011
Last visit: 11/24/2014
Posts: 6
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

the images are hosted here


C:\Archivos de programa\Siemens\SIMATIC WinCC flexible\WinCC flexible Images\
Top
  4/19/2012, 1:11 PM
Joined 2/13/2012
Last visit: 11/18/2014
Posts: 9
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
How to do that? because my HMI hang on "Startup in progress". Please explan procedure.
I have MP377 15" touch same problem. Sometime hang at partition 0 and sometime hang at partition 1.Rnf:lblSmileyTooltip_  think
Top
  4/19/2012, 1:21 PM
Joined 4/22/2010
Last visit: 11/27/2014
Posts: 5343
Rating:
Rated: Excellent [4.27 out of 5 / rated 545 time(s)]. (545) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

See 2nd Link Darius posted.

Regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum sections for your questions.
Top
  4/20/2012, 4:15 AM
Joined 2/13/2012
Last visit: 11/18/2014
Posts: 9
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
2nd link need boot up complete. but now it not complete. Cannot do everything only pingRnf:lblSmileyTooltip_  think
Top
  4/20/2012, 7:12 AM
Joined 5/28/2008
Last visit: 11/27/2014
Posts: 3282
Rating:
Rated: Outstanding [3.71 out of 5 / rated 596 time(s)]. (596) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,
In case of this panel in warenty period, please call your seller or local Siemens representative to replace it.

Ayman Elotaify
MISC Egypt
www.miscegypt.com
Top
  4/20/2012, 7:24 AM
Joined 4/22/2010
Last visit: 11/27/2014
Posts: 5343
Rating:
Rated: Excellent [4.27 out of 5 / rated 545 time(s)]. (545) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Here are the steps:

manual chapter 7 wrote:

Proceed as follows:

1. When updating the operating system with reset to factory state only:

Switch off power to the HMI device.

2. On the configuration PC, select the "Communication settings" command in the menu

"Project > Transfer" in WinCC flexible.

The "Communication Settings" dialog opens.

3. Select the type of HMI device.

4. Select the type of connection between the HMI device and the configuration PC, then set

the connection parameters.

5. Close the dialog box with "OK".

6. Select the "OS Update" command from the "Project > Transfer" menu in WinCC flexible.

7. Select update the operating system with restoring the factory state by setting the "Reset to factory settings" check box
8. Select the HMI device image file "*.img" under "Image path".

The HMI device image files are available under "WinCC flexible Images" in the

WinCC flexible installation folder or on the WinCC flexible installation CD.

The output area provides information on the version of the successfully opened HMI device image file.

9. In WinCC flexible, select "Update OS" on the configuration PC to run the operating system update.

10. When updating with reset to the factory state only:

Switch on the power supply to the HMI device.

12. Follow the instructions in WinCC flexible.

A progress bar indicates the progress of the operating system update.



If that doesn't work you have to send the Panel for repairsad

Regards,

Marcjan