Regarding MCCB of Series 3 VT and 3 VL:-

I have two queries in this regards:-
1. [snip] ...

2. Does it makes any difference / affects protection, if we terminate mains supply on top terminals of MCCB and take O/G from bottom terminals ?? That means does direction of power flow has any affect ? What is Siemens recommendation in this regards. This query is for all MCCB's including normal Thermal Magnetic & advanced with Microprocessor based trip unit.
Awaiting your Reply.



=== Edited by CS Moderator @ 1/5/2012 12:52 AM [GMT ] ===
new subject after splitting from Regarding MCCB of Series 3 VT and 3 VL - Question 1

Top
  12/7/2012, 3:30 PM
Joined 2/4/2010
Last visit: 10/14/2014
Posts: 46
Rating:
Rated: Outstanding [4 out of 5 / rated 4 time(s)]. (4) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Arvind,

Circuit breakers must not be installed upside down, however, it does not matter if energy flow is top down or bottom up.

Best regards
Sentronix