Technical Forum

Communication / Networks

Modbus communication with Sentron PAC3100 RS485 Module to S7 400 Communication with two quary sample program

Thread Starter: SREE_4U   Started: 6/25/2011 2:20 PM   Replies: 1

« Previous thread Next thread »
Page 1 of 1 (2 items)
  6/25/2011, 2:20 PM
Joined 6/25/2011
Last visit: 8/23/2011
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
sadcry Modbus communication with Sentron PAC3100 RS485 Module . Please send the S7 400 Communication with two quary sample program



=== Edited by SREE_4U @ 6/25/2011 2:23 PM [GMT ] ===


=== Edited by SREE_4U @ 6/25/2011 2:22 PM [GMT ] ===


=== Edited by SREE_4U @ 6/25/2011 2:21 PM [GMT ] ===


Top
  6/25/2011, 4:07 PM
Joined 9/27/2006
Last visit: 6/19/2013
Posts: 4032
Rating:
Rated: Excellent [4.16 out of 5 / rated 622 time(s)]. (622) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Sree;
You will need to setup a Modbus RTU master in the S7-400 rack, which means inserting a CP 441-2 (with a Modbus master loadable driver) in the CPu rack, or a CP341 (with the same loadable driver) in a ET 200M Profibus slave, or even a 1SI Modbus module in a ET 200S system.
The Modbus master program will vary a bit depending on the selected hardware.
What hardware have you thought of using, at this point in the project?

CP 441-2: http://support.automation.siemens.com/WW/view/en/22302279

CP 341: http://support.automation.siemens.com/WW/view/en/24284824/133200

Loadable driver: http://support.automation.siemens.com/WW/view/en/4072784

ET 200S 1SI: http://support.automation.siemens.com/WW/view/en/26263724

Hope this helps,
Daniel Chartier
Top