LOGO! Output Wiring Question

Thread Starter: Darren B-K   Started: 4/14/2011 3:26 PM   Replies: 5

« Previous thread Next thread »
Page 1 of 1 (6 items)
  4/14/2011, 3:26 PM
Joined 3/1/2011
Last visit: 8/11/2014
Posts: 11
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
 
   On the 2 output terminals, does it matter which way round you wire to these.  In the manual it says the +24V should go to the right hand side terminal and the load connected to the left hand side terminal then down to neutral.  I have connected my +24V to the left hand side terminal and my load to the right hand side then to neutral.  Is this a problem?

The reason Im asking is becasue my output will not de energise.  Could this be the reason ?  Program all works fine in simulation, so must be a hardware issue. Any help appreciated.

Thanks,

Darren Rnf:lblSmileyTooltip_
Top
  4/14/2011, 5:37 PM
Joined 4/22/2010
Last visit: 8/29/2014
Posts: 5059
Rating:
Rated: Excellent [4.23 out of 5 / rated 511 time(s)]. (511) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
It would help if you write what type off Logo you use.

Best regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum sections for your questions.
Top
  4/14/2011, 6:56 PM
Joined 3/1/2011
Last visit: 8/11/2014
Posts: 11
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Its a logo pure 24V : Part No. 6ED10573BA100BA0  Type 0BA6
Top
  4/14/2011, 7:26 PM
Joined 4/22/2010
Last visit: 8/29/2014
Posts: 5059
Rating:
Rated: Excellent [4.23 out of 5 / rated 511 time(s)]. (511) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
O.k. that's the ordernumber of a complete box.
If i'm right there is a RC Logo in it.
That means it's a Relay type with clock.
If that is correct it doe'n't matter how you connect the outputs( functionally that is)

On your TD allso in the box you can see if the output is high.

Working in simulation does not mean that it will work in a real logo.

Try a simple program input to output and test again.

Best regards,

Marcjan



Problem solved?
Please let us know!

Please no technical questions by PM, use the forum sections for your questions.
Top
  4/18/2011, 1:09 PM
Joined 3/1/2011
Last visit: 8/11/2014
Posts: 11
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
blush
I found the problem.  It was my programing.  I was using the F1 button on the logo TD as an on/off switch and must of pressed it twice, as when it was off I was not able to de engergise the output Q1. Not much of an on/off switch then !  It was in my haste to get my new plc control box up and running.  Program attached for reference in case anyone else makes a similar mistake.  If I didnt press it twice it means the F1 button didnt latch even though it was set as a switch.

Thanks for your comments though.

Attachment: easy piston cycle.zip  (21 Downloads)

Top
Thank you for this post from:
  4/18/2011, 3:15 PM
Joined 4/22/2010
Last visit: 8/29/2014
Posts: 5059
Rating:
Rated: Excellent [4.23 out of 5 / rated 511 time(s)]. (511) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
The function keys are like any other digital input.
The setting switch is for simulation only, not for a real Logo.

Best regards,

Marcjan

Problem solved?
Please let us know!

Please no technical questions by PM, use the forum sections for your questions.
Top