Hello,

Is it posible to communicate from a s71200 cpu to a Lon network

Top
  2/28/2011, 6:19 PM
Joined 6/29/2010
Last visit: 1/19/2015
Posts: 112
Rating:
Rated: Excellent [4.56 out of 5 / rated 48 time(s)]. (48) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi arnie,

S7 1200 hasn't library for LonWorks protocol, but if you need, you can implement the protocol and use a CM RS 485 module.

The protocols supported are:

Through the ethernet port:
TCP/IP, ISO on TCP and in the near future, PROFINET and UDP.
Modbus TCP for PAC3200 (library).

Through the CM modules:
RS485 Modbus and USS (library)
RS232 PtP.
In the near future PROFIBUS CM module and GSM CM module.

Take a look at this link:
https://www.automation.siemens.com/mcms/programmable-logic-controller/en/simatic-s7-controller/s7-1200/communication/Pages/Default.aspx
Top
  3/1/2011, 8:49 AM
Joined 10/27/2008
Last visit: 1/12/2015
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Thanks Mr Paiva for your reply,

I find out that there is a module DP/LON link in the siemens building technology so i hope that i can make a connection with the new Profibus module for s7-1200

arnie

Attachment: DP_Lon_Link_Rev.May2003.pdf  (114 Downloads)

Top
  12/24/2011, 2:29 PM
Joined 12/29/2008
Last visit: 7/9/2014
Posts: 23
Rating:
Rated: Excellent [5 out of 5 / rated 2 time(s)]. (2) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
The phisical level of Lonwork protocol (one in ISO/OSI model) isn't RS485, but it is dedicated.
This means no possible to use standard board of S71200 to develop comunication.
Easiest way is Modbus master library on S71200 and a gateway LON-MODBUS outside.

One of the possible gatewayLON-MODBUS is protonode ( http://www.marcomweb.it/ProtoCessor/ProtoNode.aspx )
But other LON-MODBUS gateway are available on the market.



=== Edited by LucaM @ 12/24/2011 2:32 PM [GMT ] ===


=== Edited by LucaM @ 12/24/2011 2:30 PM [GMT ] ===


Top
  12/25/2011, 5:13 PM
Joined 9/8/2009
Last visit: 1/26/2015
Posts: 744
Rating:
Rated: Outstanding [3.84 out of 5 / rated 50 time(s)]. (50) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I think that LON is not open source and you can't find documentation for making a protocol stack in PLC or any other MCU, instead you have to buy a ready made module or dedicated ASIC for use with MCU.