Encoder Programming in Step 7 for ET200S Module.

Thread Starter: k.k   Started: 1/30/2011 3:19 PM   Replies: 5

« Previous thread Next thread »
Page 1 of 1 (6 items)
  1/30/2011, 3:19 PM
Joined 4/29/2010
Last visit: 6/12/2012
Posts: 40
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

In our application we need to measure and control the Equpiment travel distance in meters for that we used 24 V d c1024 ppr Incremental encoder, signal is taken to the ET200S Pulse Module.

We using ET200S 1 Count 24v DC module ( 6ES7 138-4DA04-OABO ) integrating with Step 7 software so kindly anybody reply to me how to programme and how to receive the pulse count.

I refered the Technological functions Manual in Chapter 2 but I can't get clear Idea.

Pls send if u anybody have screen shot procedure.

Thanks in advance
rgrds kk



=== Edited by O_Moderator @ 1/30/2011 4:44 PM [GMT ] ===
contact data deleted


Thanks & Regards

KK
Top
  1/31/2011, 10:38 AM
Joined 8/31/2005
Last visit: 11/21/2014
Posts: 1172
Rating:
Rated: Outstanding [3.84 out of 5 / rated 146 time(s)]. (146) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,
Did you see this?
In HWConfig you select the module and function you want to use and you set the module parameters (properties of the module).
In the S7 program you use Load and Transfer commands (or Move blocks in FDB) to transfer the data to or from the module.

Attachment: Bild1.jpg  (174 Downloads)

mfG / Best Regards

Dirk

Top
  1/31/2011, 8:40 PM
Joined 4/29/2010
Last visit: 6/12/2012
Posts: 40
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thank you for reply

In the S7 program kindly explain in detail Load and Transfer commands (or Move blocks in FDB) to transfer the data to or from the module.

I can't get clear idea to use in programme, Pls reply to me easiest way to Measure the count Pulses from the encoder.


Regards
KK

Thanks & Regards

KK
Top
  2/1/2011, 7:48 AM
Joined 3/21/2006
Last visit: 11/21/2014
Posts: 9896
Rating:
Rated: Outstanding [3.92 out of 5 / rated 1048 time(s)]. (1048) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Make one FC and one DB with a length of 16 bytes. The start address of the module is 256. This corresponding to first address for this module in hardware configuration. After calling this block (OB1) in created DB you will have all info -

DB1.DBD8 (current count value)

DB1.DBx13.0 (internal gate status).

Then you can play further with these value...

Best regards,

Hristo Mihalev

Top
  2/4/2011, 7:28 PM
Joined 4/29/2010
Last visit: 6/12/2012
Posts: 40
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Dear Sir,

I created one FC ( name FC1) & DB ( name DB9) ,In the Hardware Count module PLC start Address is PIW 312 so how to address in the FC and DB count address ?.

I am new to the  ET200 Encoder ( Count ) Module,kindly anybody reply to me at earliest.

Regards
Krishnakumar


Thanks & Regards

KK
Top
  2/6/2011, 6:11 PM
Joined 4/29/2010
Last visit: 6/12/2012
Posts: 40
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Dear All, I am new to the Encoder interface in step7 and ET200s count module, kindly anybody reply to me how to do this ? I am in under commissioning works. regards KK