Hello All,

I dont know this is a right place or not for such query but as i m working on a sinamic project this contain

1 Basic Line Module = 400 kw
2 Single Motor Module=60 amp,85amp and 132 amp for 1PH7 - motors 22kw, 28kw and 50kw

i want to know how should i calculate the cable crossection in SQMM for the cables between drive and motor.

Is there any formula or chart or link which can help me

i gone through the catlouges and technical detaills for sinamics but i found there the maximum crosssection only


regards
simatic manager
Top
  2/5/2009, 12:25 PM
Joined 2/27/2008
Last visit: 12/21/2010
Posts: 148
Rating:
Rated: Outstanding [3.7 out of 5 / rated 10 time(s)]. (10) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Dear ,

Information provided by you gives me following data.

Assuming operating voltage 400v. I may suggest following Cable Sizes(PCP)

Motor rating         Cable size

22Kw                      6sq.mm

28Kw                      10 sq.mm

50 kw                       35 sq.mm

Top
  2/6/2009, 11:33 PM
Joined 10/19/2005
Last visit: 5/9/2010
Posts: 272
Rating:
Rated: Outstanding [4 out of 5 / rated 21 time(s)]. (21) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello SM,

Obtain a copy of the D21.1 Catalog and in the Motion Connect section power cables are described.
In the 2006 edition of D21.1 see page 5/5.  Generally the column marked "C" will be suitable.

mm^2 - Amps
16        66

25        84

35        104

50        123

70 – –  155

95 – –  192

120 – –221

150 – –234

185 – –267

Hope this helps...

Top
  2/20/2009, 9:14 AM
Joined 2/21/2008
Last visit: 10/10/2014
Posts: 148
Rating:
Rated: Outstanding [3.6 out of 5 / rated 5 time(s)]. (5) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
HI
THANKS ALL FOR UR VALUABLE SUGSESTATION

REGARDS

SM
Top