Hi,
I have a simodrive 611 with a fault code of F09, is there a fault code list that I could check for trouble shooting?
Top
  10/3/2008, 1:31 PM
Joined 3/21/2006
Last visit: 1/30/2015
Posts: 9932
Rating:
Rated: Outstanding [3.92 out of 5 / rated 1054 time(s)]. (1054) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Hi

 

I use this manual: Quick Startup Guide for SIMODRIVE 611 Universal  blush. But in this manual I can't found F09 fault.sad

Or better try this one: SIMODRIVE 611 universal Function Manual

regards




=== Edited by UMENCHO @ 10/3/2008 1:40 PM [GMT ] ===


Top
  10/3/2008, 4:58 PM
Joined 10/19/2005
Last visit: 5/9/2010
Posts: 272
Rating:
Rated: Outstanding [4 out of 5 / rated 21 time(s)]. (21) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello TechDave,

There are a few versions of Simodrive 611 (e.g., 611A, 611D, 611U, etc.).  My guess is that you have a 611A drive and a main spindle drive at that (i.e., HSA - haupt spindle antreibe); therefore, you should go to www.automation.siemens.com/doconweb and download the manual called Simodrive 611 analog start up guide and turn to the appropriate section for the drive you have (i.e., HSA or AMM).

Under the HSA section I find the following and I hope this helps...:

F09 Fault, encoder system 1 (motor encoder)

Motor encoder not connected or defective

Motor encoder cable defective

Measuring circuit 1 (speed actual value sensing) defective, not correctly inserted or incorrectly equipped (P150).

The fault message can be suppressed via

P090 bit 1 from FW 2.00 onwards.


Check the encoder cable/shielding, or

Replace the motor encoder, or

Replace the control board