Technical Forum

SIMATIC S7-400 / S7-400H / S7-400F /FH

PCS7 Maintaining CPU in run Mode

Thread Starter: dmahon   Started: 2/7/2006 10:15 AM   Replies: 1

« Previous thread Next thread »
Page 1 of 1 (2 items)
  2/7/2006, 10:15 AM
Joined 2/7/2006
Last visit: 11/5/2012
Posts: 1
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

I have a project consisting of an S7 416 CPU with distributed IO. The customer requires the CPU to remain in the run mode even if one of the remote racks is powered down. I compile and download the program but the only way to keep the CPU in run mode is by deleting the fault OB's (85,86 & 122) and reinserting new OB's and the downloading them to the PLC. Is it possible to alter the settings on complie to eliminate the need of deleting the OB's.

Thanks in advance

Dmahon

Top
  2/7/2006, 10:51 AM
Joined 9/28/2005
Last visit: 5/20/2013
Posts: 3149
Rating:
Rated: Outstanding [3.53 out of 5 / rated 164 time(s)]. (164) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Dmahon,

did you already check this CIR-manual for your engineering???

http://support.automation.siemens.com/WW/view/en/14044916

regards,
Nemo