My 6RA70 D.C drive during thyristor check found fault value 13
Thread Starter: devakanish Started: 8/30/2012 10:20 AM Replies: 2

8/30/2012, 10:20 AM
|
Joined 8/30/2012
Last visit: 9/1/2012
Posts: 2
Rating:
(0)
|
(0)
|
My 6RA70 D.C drive during thyristor check found fault value 13 i.e thyristor can not be fired (X13) what could be the reason/failure
|
|
|
|

8/31/2012, 11:17 AM
|
Joined 8/25/2006
Last visit: 6/17/2013
Posts: 909
Rating:
(86)
|
(0)
|
Hello. Look at the description of F061 in the manual, chapter 10.1.2.11:
Possible causes: ♦ Firing pulse cable to relevant thyristor is interrupted ♦ Ribbon cable X101 or X102 is incorrectly inserted or interrupted ♦ Defective electronics or gating board ♦ Internal interruption in gating cable in thyristor module
|
|
|
|

9/1/2012, 1:01 PM
|
Joined 8/30/2012
Last visit: 9/1/2012
Posts: 2
Rating:
(0)
|
(0)
|
dear sir,
i checked from the manual what ever mentioned
Firing pulse cable to relevant thyristor is interrupted ♦ Ribbon cable X101 or X102 is incorrectly inserted or interrupted ♦ Defective electronics or gating board ♦ Internal interruption in gating cable in thyristor module
but all the above issues not there
i checked it what else shall i open the thyristor and verify?
any other possible reason?
thanx in advance
|
|
|
|