My 6RA70 D.C drive during thyristor check found fault value 13

Thread Starter: devakanish   Started: 8/30/2012 10:20 AM   Replies: 2

« Previous thread Next thread »
Page 1 of 1 (3 items)
  8/30/2012, 10:20 AM
Joined 8/30/2012
Last visit: 9/1/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
My 6RA70 D.C drive during thyristor check found fault value 13 i.e thyristor can not be fired (X13) what could be the reason/failure
Top
  8/31/2012, 11:17 AM
Joined 8/25/2006
Last visit: 6/17/2013
Posts: 909
Rating:
Rated: Excellent [4.21 out of 5 / rated 86 time(s)]. (86) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello.
Look at the description of F061 in the manual, chapter 10.1.2.11:
Possible causes:
♦ Firing pulse cable to relevant thyristor is interrupted
♦ Ribbon cable X101 or X102 is incorrectly inserted or interrupted
♦ Defective electronics or gating board
♦ Internal interruption in gating cable in thyristor module
Top
  9/1/2012, 1:01 PM
Joined 8/30/2012
Last visit: 9/1/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
dear sir,

i checked from the manual what ever mentioned

Firing pulse cable to relevant thyristor is interrupted
♦ Ribbon cable X101 or X102 is incorrectly inserted or interrupted
♦ Defective electronics or gating board
♦ Internal interruption in gating cable in thyristor module

but all the above issues not there

i checked it what else shall i open the thyristor and verify?

any other possible reason?

thanx in advance
Top