Is it possible to use CP340 card with IM 153-2 in software redundancy with S7-315-2DP CPU???
--Nothing is Nothing--
|
|
|
|

8/18/2012, 3:06 PM
|
Joined 9/6/2008
Last visit: 5/20/2013
Posts: 986
Rating:
(55)
|
(0)
|
Hi
Well yes you can use CP340 with R system.
Have fun...
TAGOLOVER
|
|
|
|

8/18/2012, 5:16 PM
|
Joined 5/28/2008
Last visit: 5/23/2013
Posts: 2187
Rating:
(431)
|
(1)
|
Is it possible to use CP340 card with IM 153-2 in software redundancy with S7-315-2DP CPU??? No you can not use it as CP340 is not released for software redundancy. Please have a look on the following FAQ: Hope this helps.
Ayman Elotaify
MISC Egypt
www.miscegypt.com
|
|
|
|
|
Thank you for this post from:
|

8/20/2012, 11:25 AM
|
Joined 11/24/2010
Last visit: 5/24/2013
Posts: 92
Rating:
(0)
|
(0)
|
Is it possible to use CP340 card with IM 153-2 in software redundancy with S7-315-2DP CPU??? No you can not use it as CP340 is not released for software redundancy. Please have a look on the following FAQ: Hope this helps.
I also read above mentioned FAQ but some people are suggesting us that we can use CP-340 in R-system. Pls provide me some more information???