Technical Forum

SIMOTICS

stop motor

Thread Starter: saeedplc   Started: 8/10/2012 7:55 AM   Replies: 3

« Previous thread Next thread »
Page 1 of 1 (4 items)
  8/10/2012, 7:55 AM
Joined 12/8/2010
Last visit: 3/31/2013
Posts: 147
Rating:
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
hello.

suppose that a servo motor is rotating at 1000 rmp and i give zero setpoint
to servo drive. what happen in this situation? 
is the motor stop suddenly or with deceleration time?
is the motor stoped with deceleration time if i disconnect servo on signal?

best regards.

Top
  8/10/2012, 11:19 PM
Joined 8/8/2011
Last visit: 6/18/2013
Posts: 126
Rating:
Rated: Outstanding [4 out of 5 / rated 25 time(s)]. (25) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello saeedplc,

The motor will decelerate from 1000 rpm to zero speed at a rate / time per the parameters within the servo drive ramp function generator(s).

Deputy 
Top
  8/11/2012, 5:36 PM
Joined 12/8/2010
Last visit: 3/31/2013
Posts: 147
Rating:
Rated: Good [1 out of 5 / rated 1 time(s)]. (1) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

hello.

thanks for your reply.

Are you mean that there isn't any difference between giving zero setpoint
and disconnecting "servo on signal" on stoping time of the motor?

best regards.
Top
  10/12/2012, 7:50 AM
Joined 4/23/2010
Last visit: 6/18/2013
Posts: 1148
Rating:
Rated: Outstanding [3.17 out of 5 / rated 53 time(s)]. (53) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
There is difference. When zero set point is given motor goes to zero speed from 1000 RPM with ramp down time. In case servo On is cutt off, it will not have ramp down & any control & it will coast down to zero speed.
Hope this helps.

Tell me and I will forget. Show me and I will remember. Involve me and I will understand. -Confucius
Top
Page 1 of 1 (4 items)
Actions