hi Everybody i hope you can help me.
I have project with Sentrol 3WL Circuit Breaker
but we forget the External Neutral Transformer
3WL9111-0AA21-0AA0
and i have to commissioning between the next weeks and i dont have the external transformer.
I try to get the technical characteristics for the CT, but i dont found anything. But somebody tell me that i can use a 1200A/1A CT for the nuetral, cause is the same as the G transformer specification.
The question is
Can i use another transformer with the 1200A/1A relation for the N conductor connected to the Sentron????

Thanks
Top
  8/9/2012, 11:35 AM
Joined 2/4/2010
Last visit: 4/26/2013
Posts: 45
Rating:
Rated: Excellent [4.5 out of 5 / rated 2 time(s)]. (2) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Hi,
3WL9111-0AA21-0AA0 is special CT for 3WL including Rogowski coil as sensing element, output signal is 200 mV/kA.

Input on the trip unit will not work with 1 A secondary signal of a normal CT.
Sentronix

Top