Select a different PLC in the hardware configuration. Select the 1214 dc/dc/dc with firmware that matches your device. It is probably still 2.2 if that is how it arrived. These plc devices have some programming in the firmware update system that prevents it from loading the wrong firmware.
You can probably use the online / diagnostics (near bottom of the project tree) to get online with that plc and issue a factory reset. Then you should be able to set the ip address and load your project.
It should save you some grief, but if that fails, you can use the s7-1200 tool to set the ip address without the portal. Look in the search box for "set ip address on s7-1200 without tia portal"