  7/26/2012, 4:03 PM
Joined 6/1/2012
Last visit: 8/16/2012
Posts: 21
Rating:
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Good Morning,

I thought I would post on this subject in case others run across the same issue we had when using Wonderware HMI software communicate to a S7-400H system.  For most of our values and setpoints we use in our systems, we use REAL values since it makes for more accurate math calculations.  These values would not show correctly on the screen when tagging to the Siemens nomenclature. (See Below)

The Wonderware help section was not clear on the Item Name convention for Memory tags in the Siemens PLC. For example...

SIEMENS WONDERWARE
M2.7 BOOL  MX2.7
MW10 INT MINT10
MD10 REAL MREAL10
MD10 DINT MDINT10

More on this topic can be found under the HELP section in the Archestra System Management Console under ITEM NAMING and FLAG BYTES.
Top
Thank you for this post from:
  8/7/2012, 12:17 PM
Joined 8/7/2012
Last visit: 8/11/2012
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
thanks for your valuable information. Please also advise the addressing syntax for V-memory address VD0. I tried with DB1,D0 but it is not showing proper value.
your reply will help me a lot :)
regards
manasee



=== Edited by ManaseeK @ 8/7/2012 12:17 PM [GMT ] ===


Top
  8/7/2012, 1:51 PM
Joined 3/21/2006
Last visit: 5/21/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Your way is correct. It should be VD0->DB1,D0. Perhaps you have a wrong scalling or representing of type of tag. For your reference an example  http://fa.sammicomputer.co.kr/TECH/html/t002006.htm.togue
To add a item names in case of using DBs.
in case of BOOL: DB100.DBX0.0 -> DB100,X0.0
               INT:     DB100.DBW10 -> DB100,INT10
               DINT    DB100.DBD20 -> DB100,DINT20
               REAL   DB100.DBD30 -> DB100, REAL30
               STRING DB100.DBB40 (let's assume in DB we have 10 string until DBB49) -> DB100,STRING (40,10)...
Important thing is also on the same time to make corresponding selection of tag type.

Best regards,
Hristo Mihalev



=== Bearbeitet von UMENCHO @ 08.08.2012 10:03 [GMT ] ===


=== Edited by UMENCHO @ 8/7/2012 1:52 PM [GMT ] ===


Top