Dear sir,

       We have a PLC S7-400 for that, how to take  a loaded program to back-up? how to find the firmware for my PLC? and in my configuration rack CP-413 communication module is their using this module how to connect PC to PLC their is any special IP adress need for that? please explain i am new for this world.

with regads
putta
Top
  7/20/2012, 7:48 AM
Joined 4/22/2010
Last visit: 5/23/2013
Posts: 3208
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Users with special expertise supervising conferences
Rated: Above avarage [3 out of 5 / rated 1 time(s)]. (1) 
Hello,

To make a backup off the program:

1. make sure you can connect to CPU, check settings in PG/pc interface.
2. make a new empty project and select in the TAB PLC upload station, follow the messages on the screen.
You now have the program and hardware config on your PC, but there are no symbols, comments and variable names in it, so hard to read.
Better get the original program from writer.

The firmware can be read in the Hardware Config.

I have attached a few pictures to show.

About that CP-413, can you give us the 6ES7.... number written on it?

Regards,

Marcjan

Attachment: firmware.pdf  (26 Downloads)



=== Edited by Marcjan @ 7/20/2012 8:03 AM [GMT ] ===



Problem solved?
Please let us know!

Please no technical questions by PM, use the forum!

Top
  7/20/2012, 12:11 PM
Joined 11/1/2011
Last visit: 3/8/2013
Posts: 58
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Marcjan schrieb:
Hello,

To make a backup off the program:

1. make sure you can connect to CPU, check settings in PG/pc interface.
2. make a new empty project and select in the TAB PLC upload station, follow the messages on the screen.
You now have the program and hardware config on your PC, but there are no symbols, comments and variable names in it, so hard to read.
Better get the original program from writer.

The firmware can be read in the Hardware Config.

I have attached a few pictures to show.

About that CP-413, can you give us the 6ES7.... number written on it?

Regards,

Marcjan


Dear sir,

   sorry my CP model is  CP-443-1GX20-0XE0.

with regards
putta

Attachment: IMG_3331.JPG  (15 Downloads)

Top
  7/20/2012, 12:45 PM
Joined 4/22/2010
Last visit: 5/23/2013
Posts: 3208
Rating:
Rated: Excellent [4.11 out of 5 / rated 295 time(s)]. (295) 
Users with special expertise supervising conferences
Rated: Above avarage [3 out of 5 / rated 1 time(s)]. (1) 
Hello,

You can reach that module with PG setting at TCP/IP------your Network card.
The CP has it's own IP-adress, programmed in the hardware config.
But if you select accesible nodes you must be able to see it in a list.
You can try allso to reach the module by it's Mac-adress (written on the front off module under the lan connectors.

Regards,

Marcjan