Problem with OP 177B Panel

Thread Starter: eligodoy   Started: 7/17/2012 1:31 AM   Replies: 7

« Previous thread Next thread »
Page 1 of 1 (8 items)
  7/17/2012, 1:31 AM
Joined 7/17/2012
Last visit: 7/19/2012
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi, The power fail when I was updating the panel, and now, it only show primary screen with Bootloader version 1.0 and then go black! I try to upload or upgrade OS using Wincc with MPI cable and Ethernet and dont work, what can I do? Thanks for help!sad



=== Edited by eligodoy @ 7/17/2012 1:31 AM [GMT ] ===


Top
  7/17/2012, 5:42 AM
Joined 3/21/2006
Last visit: 5/14/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Try it with "Reset to factory settings" option from http://support.automation.siemens.com/WW/view/en/26437978

Best regards,
Hristo Mihalev
Top
  7/17/2012, 10:57 PM
Joined 7/17/2012
Last visit: 7/19/2012
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi Umencho, I try all reset with a MPI/USB cable and dont work. I need the RS232/PPI cable?
Top
  7/18/2012, 10:57 AM
Joined 9/5/2011
Last visit: 5/17/2013
Posts: 2549
Rating:
Rated: Outstanding [3.83 out of 5 / rated 131 time(s)]. (131) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Yes, do you need a RS232/PPI multi-master cable or USB/PPI cable for the reset.

You can find these cable in the following FAQ.

What transfer options are available in the various operator panels?

Tweety
Top
  7/18/2012, 3:01 PM
Joined 7/17/2012
Last visit: 7/19/2012
Posts: 3
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
laughThanks very much, I check the list, and the only option for Booting (because have damaged operating system) is the 90° Winkel (9 pol. 1:1) 6AV6 671-8XD00-0AX0 or the RS232/PPI 6ES7 901-3CB30-0XA0.

  If I can understand, no other cable is used to repair the panel. Just that. My USB / MPI is useless in this case.
 
 This 90º Winkel is a converter ( https://support.automation.siemens.com/WW/llisapi.dll?aktprim=0&lang=en&referer=%2fWW%2f&func=cslib.csinfo&siteid=cseus&load=content&groupid=4000003&switchLang;22150270;5.x=34&switchLang;22150270;5.y=4&extranet=standard&viewreg=WW&nodeid0=10805566&objaction=csview ), I need another cable to complete the repair?

I'll get that cable and what else? Thanks for the help Tweety!



=== Edited by eligodoy @ 7/18/2012 3:19 PM [GMT ] ===


=== Edited by eligodoy @ 7/18/2012 3:10 PM [GMT ] ===


Top
  7/19/2012, 10:54 AM
Joined 9/5/2011
Last visit: 5/17/2013
Posts: 2549
Rating:
Rated: Outstanding [3.83 out of 5 / rated 131 time(s)]. (131) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello eligodoy,

You need this cable RS232/PPI 6ES7 901-3CB30-0XA0 for Operating system update with Reset to factory settings. The procedure of this is described in the following FAQ.

http://support.automation.siemens.com/WW/view/en/26437978

Tweety
Top
  11/5/2012, 4:06 PM
Joined 3/3/2010
Last visit: 11/5/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
hi all again! I found the cable, and start reset, the system try to read operator panel, but fail, the prosave say me:
 "Failed to determine the speed"

I change speed in prosave several times but dont work, in the cable adapter pins too. What can i do?

Some idea? thx for help. 
Top
  11/6/2012, 11:10 AM
Joined 9/5/2011
Last visit: 5/17/2013
Posts: 2549
Rating:
Rated: Outstanding [3.83 out of 5 / rated 131 time(s)]. (131) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Eli Godoy,

You do not use any USB adapter for the transfer to OP177B.

Using USB RS232 adapters and USB Ethernet adapters
When using the RS232/PPI Multi-Master cable, zero modem cable or Ethernet connections, you can only use the "real" interfaces for project transfer.
"Real" interfaces are interfaces without implementation via USB. This means that you cannot use any "USB to serial" or "USB to Ethernet" adapters.
See the following link.
What transfer options are available in the various operator panels?

If you are using high bit rates, then you must implement the RS232/PPI multimaster
cable with "E-Stand 03" (development status 03) or higher.
You see in the following link, which settings do you need with RS232/PPI multimaster
cable. see the point 4 --> 1.2

How do you do an operating system update (OS update) on operator panels?

Tweety
Top