DC converters SIMOREG
6RA80 auto current controller optimisation
Thread Starter: DK. Started: 7/9/2012 8:07 AM Replies: 2

7/9/2012, 8:07 AM
|
Joined 12/28/2007
Last visit: 3/16/2013
Posts: 20
Rating:
(0)
|
(0)
|
| | | Dear All,
I am using below drive and when I tries to optimise armature current controller in auto (P50051=25) actual armature current goes up to 240% of rated motor current (p50100).
Drive Number - 6RA8025-6DS22-0AA0-Z Drive rating - 60A & 415V P076 = 70% = 41.92 Amp P50100 = 38A
During P50051=25 armature actual current went up to 92Amp. (r50117 = 220% = 92Amp ) (r50019 = 240% = 92Amp)
Kindly let me know why such things should happened because as per manual during current controller optimisation in auto armature current will rise up to 75% of motor rated current.
In 6RA70 I never face such problem.
Thanks & Regards,
DK
|
|
|
|
|

7/10/2012, 7:05 AM
|
Joined 4/23/2010
Last visit: 5/17/2013
Posts: 1148
Rating:
(53)
|
(0)
|
Hello, Before starting otimisation, have you adjust the rated unit currents? Please check the attached sheet.
Tell me and I will forget. Show me and I will remember. Involve me and I will understand. -Confucius
|
|
|
|

7/14/2012, 5:39 AM
|
Joined 12/28/2007
Last visit: 3/16/2013
Posts: 20
Rating:
(0)
|
(0)
|
hello...
everything was setted well... afetr auto optimisation I did the manual optimsation of current controller and step responces OK howevevr again I tried to do auto optimisation then actual current goes upto 220%. Generally it must go up 70% and some peaks (spikes) can go up to 120% as my experince in 6RA70.
Kindly do the needful.
Thnks & regards,
DK
|
|
|
|