Dear Experts,

I am using Siemens S7-300  ,CPU314C-2 PN/DP PLC in out lab to control one multivariable process. We have a level sensors having sensor output voltage range as 0-5 V which will be my AI to PLC.Also in order to control level we have manipulated variable as pump voltage(0-10V) which will be AO from PLC.

I have gone through the user manual for wiring diagrams of  Internal AI/AO/DI  module of this PLC(DI8x 24DC-AI5/AO2 x12 bit) in order to connect level sensor as AI01 and AO01 as pump voltage.I think i made the wiring connection as suggested in manual but stil neither AI nor AO is working. Following are my questions:

1. Does internal AI/AO module requires supply voltage?
2. If anyone has used above mentioned AI/AOmodule  for voltage sensors (not current measurment) ,then can you please share wiring diagram for such module.

I have total 4 level sensors and 2 pump to control. I plan to use following configuration:
AI00-Level 1
AI01-Level 2
AI02-Level 3
AI03-Level 4

AO00-Pump 1
AO01-Pump 2

Thanks,


Top
  04.07.2012, 18:16
Beigetreten am: 03.07.2011
Letzter Besuch: 04.05.2013
Beiträge: 63
Bewertung:
Bewertung: keine [0 von 5 / 0 mal bewertet]. (0) 
Bewertung: keine [0 von 5 / 0 mal bewertet]. (0) 

 Hi VD1,

         Are you read the correct configured AI address in the user programming, please tell in yours AI reading values and there in any SF in yours CPU,

 

   RegardsRnf:lblSmileyTooltip_

 

   




=== Edited by Strongs @ 7/4/2012 6:38 PM [GMT ] ===


Top
  16.07.2012, 04:09
Beigetreten am: 20.08.2009
Letzter Besuch: 03.08.2012
Beiträge: 69
Bewertung:
Bewertung: Überdurchschnittlich [3 von 5 / 4 mal bewertet]. (4) 
Bewertung: keine [0 von 5 / 0 mal bewertet]. (0) 
Dear VD1,

I hope you have parametertized the Analog IOs in Hardware Configuration console as per your requirements. i.e., Selecting channels as Voltage inputs, 0-10 vdc.
(As you also might be knowing that integrated Analog IOs have voltage range of +/-10 vdc.)

I hope you are using Analog IO address as per Hardware configuration!!!!Rnf:lblSmileyTooltip_

Also find the link from where you can download the manual for your CPU and you will also find the integrated IO wiring diagram inside on page 277.

http://support.automation.siemens.com/WW/view/en/12996906

or else download this "SIMATIC S7-300 CPU 31xC and CPU 31x: Technical specifications" manual from automation.siemens.com.

or else find the attachement of the page 277.

I hope you will find the way.
Vishp.Rnf:lblSmileyTooltip_

Dateianhang: CPU314C-2 AI-AO connections.pdf  (51 Downloads)



=== Edited by VishP @ 7/16/2012 4:10 AM [GMT ] ===



Top
  17.07.2012, 10:23
Beigetreten am: 29.11.2006
Letzter Besuch: 29.04.2013
Beiträge: 46
Bewertung:
Bewertung: Gut [1 von 5 / 1 mal bewertet]. (1) 
Bewertung: keine [0 von 5 / 0 mal bewertet]. (0) 
Dear VD1

first in hardware configuration when you put the AI card  you should put the current parameter of your transmiter  for example is 2wire or 4wire transmiter,etc and after beside of the card also you should change the jumper to be same as the hardware configuration.


Best regard
Siagalis Sakis 