i have a simovert with order 6se7033-2eg60 .i replaced a cuvc board in this drive.i done quick commissioning drive setting power section and all of my setting are ok. it is terminals command and setpoint source .
but i have bad problem when i run motor by terminal first vdc link 525vdc but afew second vdc 406vdc and drive displays f008 and stop motor.
i check all of parameters vdc . my cuvc is new. i donot what do i?
Hi, please confirm if this problem (F008) existed before exchanging the CUVC card.
Also, it is not clear that the DC voltage you mention is measured (with a meter) from the DC actual, or if it is a parameter display (r006) please make sure that both match exactly.
I suspect that 1 phase of the rectifier is not functioning, it is possible for the DC Link voltage to reach full voltage with only two phases of the rectifier, HOWEVER, as soon as any load is present, the voltage drops sharply. I recommend using three current clamps on the input phases to determine which one is not drawing any (much) current and repair.