STEP 7 (TIA Portal)
Local data stack access S7-1200
Thread Starter: mosekjar Started: 5/27/2010 2:15 PM Replies: 2

5/27/2010, 2:15 PM
|
Joined 3/18/2009
Last visit: 2/6/2012
Posts: 1
Rating:
(0)
|
(0)
|
I want to access the local data stack in a FB, but is not allowed, wonder why. "Symbolic access only" is not enabled.
|
|
|
|

6/28/2012, 10:39 AM
|
Joined 6/27/2012
Last visit: 4/19/2013
Posts: 1
Rating:
(0)
|
(0)
|
I need to do the same thing! Please help!
|
|
|
|

7/5/2012, 5:37 PM
|
Joined 8/13/2010
Last visit: 2/7/2013
Posts: 10
Rating:
(0)
|
(0)
|
Hello
Create a tag on the Temp tipe and call it by the name you gave it or if you want to access directly an absolute tag when creating FB in a 1200 controller select the STANDARD instead of the OPTIMIZED in the Block Acess. In that way all tags will be referenced has in the S7-300 and you can already do what you want.
|
|
|
|